Communication bet S7-400 and PC using NI opc server

prasad.shukre

Member
Join Date
Mar 2009
Location
surat
Posts
1
Hi All,

I am developing a SCADA for siemens S7-400( 412.2) plc. For this project i used NI opc server to build scada. My problem is that NI opc server support for serial, ethernet or modem. But siemens stopped their production for MPI serial adapter. IN NI opc server i don't have any settings to configure USB MPI adapter. How will i configure USB MPI adapter in NI opc server? Is siemens povide some drivers which support USB for NI opc Server?? Or there are another hardware (except Ethernet module)which can i use??


Prasad
 
There is CP5611 (PCI), CP5621 (PCI express) and CP5711 (USB).
They all require that you use Simatic Softnet, and not the NI OPC server. The common Siemens PC Adapter USB will not work with Simatic Softnet.

There are also 3rd party Ethernet/MPI adapters. Look for Deltalogic and IBH. I dont know if NI will work with any of these. If not, they have their own OPC servers.

Since the NI software supports ethernet, then you could add a CP443-1 to the S7-400 rack. Expensive though.
 

Similar Topics

problem in a communication that lost bet. S5 135U (ALARM S3964RDDE SERVER) & In Touch Hi all experts and members ...
Replies
0
Views
2,129
Hello All! I am writing today because I cannot figure this out for the life of me. Another site I am affiliated with keeps having their slc 5/03s...
Replies
13
Views
196
Hello, I am currently in the final week of my internship and I have encountered issues with communication between a PowerFlex 700 variable...
Replies
3
Views
84
Hi all. I have a Modbus ProSoft module in my setup with a capability of 30 clients (0-29), which I'm trying to monitor the Ethernet Connection...
Replies
0
Views
43
Hi folks, I have a Controllogix in communication with a zigbee coordinator using Logix AIO for modbus tcp. This zigbee coordinator have 3 slaves...
Replies
10
Views
334
Back
Top Bottom