Communication bet S7-400 and PC using NI opc server

prasad.shukre

Member
Join Date
Mar 2009
Location
surat
Posts
1
Hi All,

I am developing a SCADA for siemens S7-400( 412.2) plc. For this project i used NI opc server to build scada. My problem is that NI opc server support for serial, ethernet or modem. But siemens stopped their production for MPI serial adapter. IN NI opc server i don't have any settings to configure USB MPI adapter. How will i configure USB MPI adapter in NI opc server? Is siemens povide some drivers which support USB for NI opc Server?? Or there are another hardware (except Ethernet module)which can i use??


Prasad
 
There is CP5611 (PCI), CP5621 (PCI express) and CP5711 (USB).
They all require that you use Simatic Softnet, and not the NI OPC server. The common Siemens PC Adapter USB will not work with Simatic Softnet.

There are also 3rd party Ethernet/MPI adapters. Look for Deltalogic and IBH. I dont know if NI will work with any of these. If not, they have their own OPC servers.

Since the NI software supports ethernet, then you could add a CP443-1 to the S7-400 rack. Expensive though.
 

Similar Topics

problem in a communication that lost bet. S5 135U (ALARM S3964RDDE SERVER) & In Touch Hi all experts and members ...
Replies
0
Views
2,128
Hi folks, I have a Controllogix in communication with a zigbee coordinator using Logix AIO for modbus tcp. This zigbee coordinator have 3 slaves...
Replies
0
Views
29
Hello, i am using profibus as communication between plc and fanuc arm. I can easily send inputs from plc to arm, but i can't monitor any outputs...
Replies
0
Views
29
I have Woodward Controller EASYGEN-3500XT and Phoenixcontact make IO CAN-CUPLER part no: 2702230, Analog Input card: 2861412, Analog Output Card ...
Replies
0
Views
39
Hello Everyone, I have a issue with communication between two different PLCs. So here is the facts, The Master PLC is Guard Logix 5069 with IP...
Replies
4
Views
98
Back
Top Bottom