What happens if you set the Message Timeout in an MSG block to zero? Does it ignore the timeout and stay enabled?
Heres the situation: We are communicating over Modbus from a ML1100 to PF700 drives. If one drive is powered down then turned back on, the PLC will not re-establish communications. I found the message timeout set to 0 in the MSG block for that drive. Could this be the cause of the problem? The other drive will re-establish comms just fine and it's MSG timeout is set to 1. Unfortunately I am 3 hours from the site and did not find that discrepency until leaving. The tech at the site claimed he tried changing the timeout to 1, with the same results.
Any ideas?
Heres the situation: We are communicating over Modbus from a ML1100 to PF700 drives. If one drive is powered down then turned back on, the PLC will not re-establish communications. I found the message timeout set to 0 in the MSG block for that drive. Could this be the cause of the problem? The other drive will re-establish comms just fine and it's MSG timeout is set to 1. Unfortunately I am 3 hours from the site and did not find that discrepency until leaving. The tech at the site claimed he tried changing the timeout to 1, with the same results.
Any ideas?