Hi everyone, hope you can help me with this

I have a S7-1200 and 3 ET200M, I want to connect 2 Siwarex U(weighing module) to each ET200M and another 2 for the S7-1200, do anybody knows if that's possible?

There's a diagram in the following link

http://imgur.com/a/aNM0o


thanks in advance

:)
 
Thank you for your answer, it was really helpful

is it possible to have the connections showed in the diagram if I use
the S7-1200 and WP231?

Best regards
 
No, You can't insert WP231 in ET200M, they have to be connected directly til a S7-1200 PLC ( you can have WP231 as Stand-alone, but then you will not have access to all parameters )
If you instead of your ET200M place a S7-1200 with the weighing modules, you can have a Master PLC with I-devices, then you will have access to all paramerters in your WP231

S7-1200 - WP231.jpg
 

Similar Topics

Hi, Is there a "rule of thumb" for Siemens logging capacity? By this I mean, if you are logging: 1 x data tag Floating point format Once per...
Replies
1
Views
1,841
The past week we received a new piece of equipment from Germany which utilizes siemens controls. Typically in our company we use A.B. controls for...
Replies
4
Views
39
Hello I have a s7-1200 and I would like to read the tags present in this controller with my controllogix controller. The two controllers don't use...
Replies
5
Views
99
Hi need help why this “failure 5 emergency stop “ appears at every startup in the morning ? Have to shut off main switch at least 10 times on...
Replies
19
Views
281
i have two plc 1. s7-1212dc/dc/dc ip; 192.168.0.1 2. s7-1500 1513-1pn ip; 192.168.3.2 i need to get data from plc1 to plc2. any idea how to do...
Replies
5
Views
97
Back
Top Bottom