SLC500 CUP power flicker

Hello everyone,

I have a SLC 5/03 with two racks, the first with 10 I/Os and the second with 12. The CPU intermittently restarts looking like it lost power . It's very quick but enough to reset all the outputs. Sometimes it happens a few times in a row and then it could be another half hour or more with nothing.

Replaced the power supply and CPU with spares (used), problem persisted. Downloaded blank program with inputs active and outputs off, the problem disappeared or so it seemed.
Downloaded the original program and the problem reappeared.


Any ideas?
  Reply With Quote
Old July 12th, 2018, 01:39 AM   #2
GaryS
Member
United States

GaryS is offline
 
GaryS's Avatar
 
Join Date: Aug 2003
Location: Lancaster Pa.
Posts: 718
The fact that it restarts is puzzling
I have seen this happen when the math overflow bit is set when the rolls over from the last line to first line. That will usually cause the processor to fault and just stop not restart.
I that case the answer is simple on the last line of program put an unconditional unlatch of the math overflow bit.
The problem is definitely in the program someplace maybe an indirect address overflow or pointing to an invalid address. The 500's can only access a file size of 250 elements 0 to 249
I know that will cause then to crash maybe when it crashes the index resets to 0 on reload.
I hope this helps let us know what you find.
  Reply With Quote
Old July 12th, 2018, 05:56 AM   #3
Aabeck
Member
United States

Aabeck is offline
 
Aabeck's Avatar
 
Join Date: Feb 2013
Location: Detroit
Posts: 1,007
It could be an intermittent short in the rack, either the backplane itself or one of the cards shorting out. I have had problems with analog cards causing shorts.

I would start swapping one IO card at a time, if you can swap it with a card on the second rack that would be best - if it is that card then the CPU will fault because the second rack shuts down, and then it won't restart. If this happens replace the card you put in the second rack.

If none of the cards are doing it I would then try the backplane.

Another thought - is it a P1 or P2 power supply that may be too small for the rack? Try a P4 as a test.
__________________
Never underestimate the quality of idiots that will be running your machines
http://aabeck.com
  Reply With Quote
Old July 12th, 2018, 06:03 AM   #4
Christoff84
Lifetime Supporting Member + Moderator
Canada

Christoff84 is offline
 
Christoff84's Avatar
 
Join Date: Jun 2006
Location: Cambridge, ON
Posts: 380
Is it a 24 volt power supply? Could there be an issue with the circuit, where the 24V drops low on energising some output and then clears when the slc loses power?
  Reply With Quote
Old July 12th, 2018, 07:05 AM   #5
rdrast
Lifetime Supporting Member
United States

rdrast is offline
 
rdrast's Avatar
 
Join Date: Apr 2003
Location: South Carolina Lowcountry
Posts: 5,242
Could be a backplane issue. Have you changed the backplane?
__________________
------------------------------------
How to ask questions the SMART Way!

Look First, Ask Second!

  Reply With Quote
Old July 12th, 2018, 10:03 AM   #6
kalabdel
Member
Canada

kalabdel is online now
 
Join Date: Feb 2015
Location: Ontario
Posts: 341
Thanks guys. I am heading back today for a second look. The error has to do with I/O but I forgot to take a screenshot or it and will do that later.
The power supply is P2 120VAC to 24VDV and the 24 is feeding an analog sensor of some sort as I see the wire going somewhere and coming back to an analog input. I will trace it today. Does loading a blank program and not having issues point somewhere?

Edit: it’s running well today and I don’t want to shut them down again. I will recommend replacing the backplane and take it from there.

Thanks

Last edited by kalabdel; July 12th, 2018 at 10:06 AM.
  Reply With Quote
Old July 12th, 2018, 12:27 PM   #7
OkiePC
Lifetime Supporting Member
United States

OkiePC is offline
 
OkiePC's Avatar
 
Join Date: Mar 2005
Location: ENE of Nowhere Oklahoma
Posts: 9,858
Quote:
Originally Posted by kalabdel View Post
...
The error has to do with I/O but I forgot to take a screenshot or it and will do that later.
The power supply is P2 120VAC to 24VDV and the 24 is feeding an analog sensor of some sort as I see the wire going somewhere and coming back to an analog input. I will trace it today. Does loading a blank program and not having issues point somewhere?
Probably not, but I suppose if there is a card that only acts up when called to do something by the program it could be a factor. Backplane failures are pretty rare, but hard to figure out and they do happen. I think it is more likely that one of the cards has a problem. Trapping that exact fault code is valuable. If there is an HMI, I try to display the error details and log them to an alarm history.
__________________
It's not all the variables I am most concerned with, it's the undiscovered constants.
  Reply With Quote
Old July 12th, 2018, 01:52 PM   #8
Aabeck
Member
United States

Aabeck is offline
 
Aabeck's Avatar
 
Join Date: Feb 2013
Location: Detroit
Posts: 1,007
Quote:
Originally Posted by kalabdel View Post
... the 24 is feeding an analog sensor of some sort as I see the wire going somewhere and coming back to an analog .
I do not ever use the 24 volts coming off the power supply to power anything - even a single proxy. One short or wiring problem on the line and the PLC shuts down. Exactly as you are having happen.

Once the 24 volts leaves the control panel it could have something tapped into it that someone saw 24 volts and didn't know where it came from.

Put in a small 24 power supply to power that/those sensors.
__________________
Never underestimate the quality of idiots that will be running your machines
http://aabeck.com
  Reply With Quote
Old July 12th, 2018, 03:13 PM   #9
Ken Roach
Lifetime Supporting Member + Moderator
United States

Ken Roach is offline
 
Ken Roach's Avatar
 
Join Date: Apr 2002
Location: Seattle, WA
Posts: 14,161
That +24V auxiliary power supply terminal on the 1746-P2 is only rated to supply 200 mA. I've definitely seen a short circuit on that cause the PSU to "crowbar" and shut down the PLC.

Replacing that source with a standalone 24V DC power supply would quickly exclude that circuit as a suspect. Add a little 1/2A fuse for extra diagnostic evidence.
  Reply With Quote
Old July 12th, 2018, 03:44 PM   #10
AznerGG
Member
Cuba

AznerGG is offline
 
Join Date: Jul 2018
Location: Mayabeque
Posts: 7
Smile

Hi, let me see if I can help you, your CPU seems to be restarting every few minutes, then you must try without I/O modules to discard that there any problem with them, if the problem persist then you must check the code because maybe you are making an overflow, I hope be helpful to you and keep me in touch,
  Reply With Quote
Old July 12th, 2018, 04:35 PM   #11
Aabeck
Member
United States

Aabeck is offline
 
Aabeck's Avatar
 
Join Date: Feb 2013
Location: Detroit
Posts: 1,007
Quote:
Originally Posted by kalabdel View Post
Does loading a blank program and not having issues point somewhere?
If the analog sensor is sensing something that would be off, or 0, when the right PLC output is off [say a pressure transducer that gives 0-20mA that is giving 0mA when the pump or solenoid valve is off] then when you energize the pump or valve the transducer starts putting out a signal and overloads the -P2. Same thing if it's a 0-10V signal.

Or the output lead from the transducer is shorted to ground somewhere in the run or inside the transducer and that would bring down the power supply when it tries to output a signal to a grounded lead.
__________________
Never underestimate the quality of idiots that will be running your machines
http://aabeck.com
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
switching proportional valve power supply causing vibration sensor output spikes? V0N_hydro LIVE PLC Questions And Answers 6 March 22nd, 2016 04:14 PM
Merger External & internal power for Gas Detector geragai LIVE PLC Questions And Answers 4 February 11th, 2012 06:58 PM
Common 0V only on 2 x 24VDC power supplies qwsoftware LIVE PLC Questions And Answers 7 December 14th, 2009 07:45 PM
PLC to manage renewable power sources jaraujo1 LIVE PLC Questions And Answers 4 September 16th, 2009 10:15 AM
slc500 power up jthornton LIVE PLC Questions And Answers 2 July 8th, 2002 11:27 AM


All times are GMT -5. The time now is 12:29 AM.


.