harryggianakis
Member
OP
AGill..., The acceptable 'fail-safe' position of our process operation is the valves are supposed to open when the hazard is present (i.e. opening the valves would mitigate this hazard). As such (i.e. and if I understand DTT vs. ETT circuitry design properly), a loss of power in a DTT circuit would cause those valves to open. In an ETT circuit, applying power would cause the valves to open.
So, if we used a DTT circuit, we would have to build-in the necessary redundancies to ensure that a power outage (and in our case, loss of building compressed air to the valves as well) would not open the valves. Why? Because the loss of these utilities (i.e. power, air) during normal process operation would basically result in lost production/significant downtime for us. The valves only must open if the process parameter that I mentioned before exceeded a certain threshold (i.e. when the hazard started to become present).
In an ETT circuit design, it sounds like a power outage would pose certain difficulties. Even if the outage caused all process equipment & field devices to go to their 'fail-safe' position (i.e. to shut down all material transfer and stop any process heating), the SIL 1 safety interlock might still be needed because the hazard could still potentially introduce itself into the process operation under these 'fail-safe' conditions (even though the risk of this happening is low).
Concerning the power/compressed air redundancies that I mentioned above for a DTT circuit design, I'm wondering if the cost of putting these additional redundancies into the DTT circuit would be offset by the cost of putting in the end of line monitoring to ensure circuit integrity in an ETT design. Any thoughts from the group? Would those costs be comparable?
mk42..., Sounds like you have a lot of experience with DTT's in machine safety. Any experience/guidance with using DTT's in process safety applications?
So, if we used a DTT circuit, we would have to build-in the necessary redundancies to ensure that a power outage (and in our case, loss of building compressed air to the valves as well) would not open the valves. Why? Because the loss of these utilities (i.e. power, air) during normal process operation would basically result in lost production/significant downtime for us. The valves only must open if the process parameter that I mentioned before exceeded a certain threshold (i.e. when the hazard started to become present).
In an ETT circuit design, it sounds like a power outage would pose certain difficulties. Even if the outage caused all process equipment & field devices to go to their 'fail-safe' position (i.e. to shut down all material transfer and stop any process heating), the SIL 1 safety interlock might still be needed because the hazard could still potentially introduce itself into the process operation under these 'fail-safe' conditions (even though the risk of this happening is low).
Concerning the power/compressed air redundancies that I mentioned above for a DTT circuit design, I'm wondering if the cost of putting these additional redundancies into the DTT circuit would be offset by the cost of putting in the end of line monitoring to ensure circuit integrity in an ETT design. Any thoughts from the group? Would those costs be comparable?
mk42..., Sounds like you have a lot of experience with DTT's in machine safety. Any experience/guidance with using DTT's in process safety applications?