Industrial Network Inspection / Analysis?

Hi All,

I'm doing mainly PLC programming but dabbling in industrial networking.

I am investigating an intermittent communication fault between a AB 1756-L82E (v33) and a RTU. PLC executes EthernetI/P Explicit messaging instructions. I have enabled logging on the RTU, is there any way to capture message logs from the PLC side?

Question part 2:
The issue has occurred once in the last month, so I doubt i'm going to find anything, and my hunch is the RTU Ethernet port has frozen up, as this has happened at other sites. However I have an order to do some on site investigation, what are some valuable documents / findings I can produce as part of the exercise / report?

I'm sure this is an exercise network ppl go though all the time:
-Wireshark capture?
-Average traffic throughput?
-iperf?
-Scan with fluke cat6 tester?

Basically wanting to show I properly investigated the issue..

Interested to see what comes back!
  Reply With Quote
Old June 23rd, 2022, 02:13 AM   #2
AlfredoQuintero
Lifetime Supporting Member
Japan

AlfredoQuintero is offline
 
Join Date: Feb 2015
Location: Yokohama
Posts: 1,055
You can use Wireshark but you need a managed switch with mirror port function to get the traffic between the PLC and the remote IO device. The Wireshark dissector for EtherNet/IP is great and usually provides a lot of good information, including decoding of error responses, so in many cases you do not need to check the specification to figure out the meaning.
  Reply With Quote
Old June 23rd, 2022, 06:33 AM   #3
TurpoUrpo
Lifetime Supporting Member
Finland

TurpoUrpo is offline
 
Join Date: May 2008
Location: Switzerland
Posts: 1,552
Check if any new machinery was installed lately and if was where their power supply is wired from. Once had a network probs cos of new installations going too near of network cables. The thing was that the errors showed up only when the machine was started (startup current peak was much higher and thus also interference was much higher), not that often as it was normally running all the time.
  Reply With Quote
Old June 23rd, 2022, 08:37 AM   #4
mk42
Lifetime Supporting Member
United States

mk42 is offline
 
Join Date: Jun 2013
Location: MI
Posts: 2,841
Wireshark will show you WHAT happened, but it won't always show you why. Managed switches with port mirroring are one good way to get a trace; there are also dedicated ethernet taps you can use that provide everything going across one cable.


I'd strongly recommend checking all cables with a tester. Some switches have one built in, otherwise you might need to buy one or hire an IT firm. It's also important to check the configuration. If some devices are fixed at 100mbps instead of autonegotiate, you can have instances where there is a mismatch and they don't communicate well, especially if it's because of a bad cable.
  Reply With Quote
Old June 23rd, 2022, 07:29 PM   #5
moistcat
Member
Australia

moistcat is offline
 
Join Date: Jun 2020
Location: Melbourne
Posts: 13
Talking

Thanks @AlfredoQuintero, @TurpoUrpo, @mk42.

I'm sure its a rack mounted greyhound switch between them so ill be sure to bring my Hirschman cable and set up a mirror port.

All else fails i have some code where the RTU can reboot itself if the heartbeat isn't seen for x seconds..
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
Industrial Automation - Stack Exchange Network staging zone carretto LIVE PLC Questions And Answers 13 May 16th, 2018 05:29 PM
Network layout suggestions Brian123 LIVE PLC Questions And Answers 5 January 23rd, 2015 05:14 PM
Redundant ControlLogix PLC control net network chapani LIVE PLC Questions And Answers 5 November 3rd, 2014 06:46 PM
PLC Network on Office Network??? d21x LIVE PLC Questions And Answers 16 September 19th, 2008 04:11 PM
Timers martin3885 LIVE PLC Questions And Answers 26 September 9th, 2005 12:51 PM


All times are GMT -4. The time now is 06:27 AM.


.