How many maximum no. of plc is possible to communicate to single FTview SE application? Is it possible to communicate the FTview SE with semens plc and schneider plc
The answer is not simple. But, there is no hard limit maximum that I know of to the number of PLCs that FTView SE can talk to.
Yes, that will work with Siemens or Schneider PLCs.
There is a practical limit on the amount of data per second.
Talking to 100 PLCs at 1 tag per second is = 100 tags per second.
Talking to 1 PLC at 100 tags per second is = 100 tags per second.
It matters if those are scattered tags, versus array tags or in a UDT, or string tags. What PLC? Is it a ControlLogix L7? Ethernet through an EN2T?
Assuming you are only using scattered DINT tags, ControlLogix L7, a single EN2T, you could probably get 50,000 tags per second.
If those tags are optimized (array or UDT), then definitely that is no problem.
As mentioned, there is no hard limit. It comes down to performance and what is acceptable.
To talk with non Rockwell controllers, you would need an OPC server. This software could run on the same machine that is acting as the HMI Server or it could run on a separate computer. You could have one computer running OPC software (OPC server) to talk to Siemen's controllers and another computer acting as the OPC server for Schneider controllers. Or they could all be running on a single computer.
By splitting it up onto separate PCs you are distributing that load and hopefully improving performance and providing an option for redundancy.
OG
I am creating a global object in FTView SE 13. I want to have a string read from the PLC and display (in this case the tagname). So lets say...
171
I want to set user security level based on the value of a tag in my PLC called "ActiveUser". That tag will contain the A-P code which we use for...
214
Hi All, we've recently upgraded from FTView SE v10 to v12. Since the upgrade we've been having a problem where the HMI is slow to update tags in...
88
Hi, I have an issue accessing tags in 3 of my plcs'. When I go to select a tag there is no folder drop down as can be seen in the photo. Any...
86
Hello, I have converted RSView 32 to FTView SE 14 (I have tested FTView 12 before as well and there were some difficulties so I moved on to...
248