Function block for analog scaling in mitsubishi gx works3

Hi Friends,
Please, who can tell me the Function Block used for scaling 4-20mA to say 0-200PSI in Mitsubishi GX Works3?
  Reply With Quote
Old May 25th, 2018, 08:37 AM   #2
BryanG
Member
United Kingdom

BryanG is offline
 
Join Date: Feb 2005
Location: Manchester
Posts: 1,249
I know nothing of GX Works3, but in general built in functions aren't always needed, write your own scaling function:


Code:
// Scaling uses this formula:
// Ov = [(Osh  Osl) * (Iv - Isl) / (Ish  Isl)] + Osl
// 
// Ov = scaled output value
// Iv = analog #Input value
// Osh = high limit OF the scale FOR the scaled #Output value
// Osl = low limit OF the scale FOR the scaled #Output value
// Ish = high limit OF the scale FOR the analog #Input value
// Isl = low limit OF the scale FOR the analog #Input value
  Reply With Quote
Old May 25th, 2018, 08:50 AM   #3
IdealDan
Member
Malaysia

IdealDan is offline
 
Join Date: May 2017
Location: MA
Posts: 262
Quote:
Originally Posted by BryanG View Post
I know nothing of GX Works3, but in general built in functions aren't always needed, write your own scaling function:


Code:
// Scaling uses this formula:
// Ov = [(Osh  Osl) * (Iv - Isl) / (Ish  Isl)] + Osl
// 
// Ov = scaled output value
// Iv = analog #Input value
// Osh = high limit OF the scale FOR the scaled #Output value
// Osl = low limit OF the scale FOR the scaled #Output value
// Ish = high limit OF the scale FOR the analog #Input value
// Isl = low limit OF the scale FOR the analog #Input value
Ok Bro. Thanks for the response.


Assuming a 4-20mA to 0-200PSI Scaling, From above: Do you mean

Osh = high limit OF the scale FOR the scaled #Output value=200psi ?

// Osl = low limit OF the scale FOR the scaled #Output value=0psi ?

// Ish = high limit OF the scale FOR the analog #Input value=20mA ?

// Isl = low limit OF the scale FOR the analog #Input value= 4mA ?


// Iv = analog #Input value (SHOULD THIS BE THE TAG)?

Last edited by IdealDan; May 25th, 2018 at 08:55 AM.
  Reply With Quote
Old May 25th, 2018, 09:56 AM   #4
BryanG
Member
United Kingdom

BryanG is offline
 
Join Date: Feb 2005
Location: Manchester
Posts: 1,249
If the Input Value is in mA, then yes.


On the PLCs I use the Input Value is the output of the Analog block and in the range of 0 to 27648. So for me Osh and Osl would be 200.0 and 0.0, Ish and Isl would be 27648.0 and 0.0. You will need to be working Floating Point numbers.
  Reply With Quote
Old May 25th, 2018, 10:19 AM   #5
IdealDan
Member
Malaysia

IdealDan is offline
 
Join Date: May 2017
Location: MA
Posts: 262
Quote:
Originally Posted by BryanG View Post
If the Input Value is in mA, then yes.


On the PLCs I use the Input Value is the output of the Analog block and in the range of 0 to 27648. So for me Osh and Osl would be 200.0 and 0.0, Ish and Isl would be 27648.0 and 0.0. You will need to be working Floating Point numbers.
You are right. Resolution 0-27648 for siemens, 0-16383 for AB SLC.
I need to figure out Mitsubishi's Resolution,
I Trust some one here will have an idea
  Reply With Quote
Old May 25th, 2018, 01:39 PM   #6
tarik1978
Member
Morocco

tarik1978 is offline
 
Join Date: Mar 2010
Location: casablanca
Posts: 316
It depends upon your IN/OUT analog module reference check this link:
https://us.mitsubishielectric.com/fa...alog-io-module
  Reply With Quote
Old May 26th, 2018, 12:40 PM   #7
BryanG
Member
United Kingdom

BryanG is offline
 
Join Date: Feb 2005
Location: Manchester
Posts: 1,249
The 0 to 27648 I gave would be for a 0-20mA signal, 4-20mA would be 5529 to 27648. 5529, is 27648 divided by 20 multiplied by 4.
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
Mitsubishi GX Developer Installation Birdman89 LIVE PLC Questions And Answers 0 June 8th, 2016 01:04 PM
GX Works2 vs GX Works3 gleblanc LIVE PLC Questions And Answers 3 March 28th, 2016 11:17 AM
"Function block call requires a function instance" when calling action in Codesys standeven LIVE PLC Questions And Answers 9 April 27th, 2015 04:11 AM
TWINCAT make function block persistent nachovr LIVE PLC Questions And Answers 4 August 22nd, 2014 05:34 AM
calling Function Block in another Function Block. rahilansari LIVE PLC Questions And Answers 9 April 21st, 2014 10:55 AM


All times are GMT -5. The time now is 04:41 PM.


.