Old May 23rd, 2018, 06:59 PM   #1
QasimFSH
Member
Australia

QasimFSH is offline
 
Join Date: Apr 2018
Location: Adelaide
Posts: 79
Using thermocouple with TM221CE16R

HI All,

I have to use thermocouple (sine the give voltage as output), and I have two analog inputs in my TM221CE16R, which are voltage dependent (0-10v, with LSB of 10mV). How can I do that? I guess I cant do this directly, does anyone know of any reliable, but a bit cheap amplifiers for Thermocouples? The other option is to but the extra cartridge for thermocouples by Schneider Electric.

Any suggestion?

Thanks.
  Reply With Quote
Old May 23rd, 2018, 08:30 PM   #2
willxfmr
Lifetime Supporting Member
United States

willxfmr is offline
 
willxfmr's Avatar
 
Join Date: Nov 2013
Location: Wisconsin
Posts: 315
https://www.omega.com
They can turn just about any signal you have to any signal you want.


Bubba.
__________________
“Now will come the nay-sayers with all the reasons why you shouldn't do this. Some of them are teachers, and some of us are doers. Besides, you have got to let the smoke out of this equipment every now and then, or it starts to clog up the chimney.”
~Lancie1
  Reply With Quote
Old May 23rd, 2018, 09:00 PM   #3
QasimFSH
Member
Australia

QasimFSH is offline
 
Join Date: Apr 2018
Location: Adelaide
Posts: 79
Quote:
Originally Posted by willxfmr View Post
https://www.omega.com
They can turn just about any signal you have to any signal you want.


Bubba.
Thanks mate, but I can get the extra cartridge for $159..
  Reply With Quote
Old May 23rd, 2018, 09:17 PM   #4
danw
Member
United States

danw is offline
 
danw's Avatar
 
Join Date: Oct 2004
Location: midwest, USA
Posts: 2,834
Look at how little voltage a thermocouple produces (approximate values):

Type K 0 to 1200 Deg C = 0 to 48.8mV, 1 Deg C change ranges from approx 0.039mV to 0.034mV
Type J 0 to 1200 Deg C = 0 to 69.5mV, 1 Deg C change ranges from approx 0.050mV to 0.057mV
Type T 0 to 400 Deg C = 0 to 20.8mV, 1 Deg C change ranges from approx 0.039mV to 0.062mV

A 0 to 10Vdc input does not have enough resolution to handle is too such small changes as 0.034mV (0.000034V)/deg. That's 10.0V/0.000034 = 294,117 parts of resolution = 100 0111 1100 1110 0110 which would require a 19 bit A/D converter to resolve a 1 degree C change in K type thermocouple, assuming no noise

The suggested alternative is to use a temperature transmitter which produces a 0-10Vdc output proportional to a scaled temperature input.

Be alert to the fact that a configuration tool for scaling the temperature (0-100 Deg? 200-400 Deg C? 0-1500 Deg C?) over the range of the output (0-10V) requires some means - keyboard and display, PC with Modem and software, HART communicator, all of which cost something.

If you're not will to spend money on a configuration tool, look for a vendor that sells a transmitter pre-configured to the range you need, or who will configure it for you for some nominal fee.

Also be aware that a grounded thermocouple with a non-isolated transmitter can create a ground loop the looks like a tempeature offset.

My suggestion is to always buy 'ungrounded' thermocouple assembly.
  Reply With Quote
Old May 24th, 2018, 06:52 PM   #5
QasimFSH
Member
Australia

QasimFSH is offline
 
Join Date: Apr 2018
Location: Adelaide
Posts: 79
Quote:
Originally Posted by danw View Post
Look at how little voltage a thermocouple produces (approximate values):

Type K 0 to 1200 Deg C = 0 to 48.8mV, 1 Deg C change ranges from approx 0.039mV to 0.034mV
Type J 0 to 1200 Deg C = 0 to 69.5mV, 1 Deg C change ranges from approx 0.050mV to 0.057mV
Type T 0 to 400 Deg C = 0 to 20.8mV, 1 Deg C change ranges from approx 0.039mV to 0.062mV

A 0 to 10Vdc input does not have enough resolution to handle is too such small changes as 0.034mV (0.000034V)/deg. That's 10.0V/0.000034 = 294,117 parts of resolution = 100 0111 1100 1110 0110 which would require a 19 bit A/D converter to resolve a 1 degree C change in K type thermocouple, assuming no noise

The suggested alternative is to use a temperature transmitter which produces a 0-10Vdc output proportional to a scaled temperature input.

Be alert to the fact that a configuration tool for scaling the temperature (0-100 Deg? 200-400 Deg C? 0-1500 Deg C?) over the range of the output (0-10V) requires some means - keyboard and display, PC with Modem and software, HART communicator, all of which cost something.

If you're not will to spend money on a configuration tool, look for a vendor that sells a transmitter pre-configured to the range you need, or who will configure it for you for some nominal fee.

Also be aware that a grounded thermocouple with a non-isolated transmitter can create a ground loop the looks like a tempeature offset.

My suggestion is to always buy 'ungrounded' thermocouple assembly.
you are righ on spot..I feel that using an RTD or thermocouple with the temperature input module(which I have to but extra) of my PLC will be the best option.
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
Logix 5000 + Phoenix Thermocouple Module cking2729 LIVE PLC Questions And Answers 5 January 26th, 2017 06:01 PM
PWM Signal from IR Thermocouple to trigger PLC Input colehan LIVE PLC Questions And Answers 2 October 8th, 2013 05:16 AM
Thermocouple signal spiltter - got such thing? flyers LIVE PLC Questions And Answers 15 April 13th, 2007 10:20 PM
It8 Thermocouple Problem parag uike LIVE PLC Questions And Answers 5 February 15th, 2006 04:06 AM
Thermocouple readout fluctuations leitmotif LIVE PLC Questions And Answers 18 March 5th, 2005 09:58 AM


All times are GMT -5. The time now is 10:09 AM.


.