Any panel I've built with contactors and overloads has been 3 phase.

I'm now quoting on one with some small single-phase loads. Definition of small, one is 0.5Amps FLC and the other 5 Amps FLC.

I've had a look at the Schneider LR97D which has a dip switch on it for single or 3 phase, but it comes with 3 legs. I've seen other discussions online whereby you use a 3 phase contactor but loop the single phase through it so that each contact is seeing the same amperage.

UK, 230V Live-Neutral.

Any other options?
__________________
Regards,

Patrick G. B.Eng MIET

Making the flashy lights flash since the 90's

SCADA - Inductive Automation Gold Integrator | PLC | Control Panels | Robotics | Training

Connect with Matrix Engineering

My son was chewing on an electrical cord, so I had to ground him. He is doing better currently and conducting himself properly. My electrical skills are quite poor, which is a shock to some people
  Reply With Quote
Old August 17th, 2022, 03:06 PM   #2
mylespetro
Supporting Member
Canada

mylespetro is offline
 
mylespetro's Avatar
 
Join Date: Dec 2015
Location: NS
Posts: 686
Quote:
Originally Posted by the_msp View Post
Any panel I've built with contactors and overloads has been 3 phase.

I'm now quoting on one with some small single-phase loads. Definition of small, one is 0.5Amps FLC and the other 5 Amps FLC.

I've had a look at the Schneider LR97D which has a dip switch on it for single or 3 phase, but it comes with 3 legs. I've seen other discussions online whereby you use a 3 phase contactor but loop the single phase through it so that each contact is seeing the same amperage.

UK, 230V Live-Neutral.

Any other options?
Doing the loop through the contactor/OL phases is how I've always seen it done. I've also done it on a couple personal projects successfully.
  Reply With Quote
Old August 17th, 2022, 03:23 PM   #3
Snyd1
Member
United States

Snyd1 is offline
 
Join Date: Jun 2018
Location: there
Posts: 217
Most documents I have seen usually have a wiring diagram for single phase motors showing looped. If you are looking to save space, the Siemens SIRUS 3RM1 motors starters have overload protection and can save some serious space in a cabinet. They are 3 phase but here is an example of how they show to wire for single phase.
Attached Images
File Type: png Siemens SIRUS Single Phase.PNG (44.3 KB, 134 views)
  Reply With Quote
Old August 17th, 2022, 03:28 PM   #4
I_Automation
Member
United States

I_Automation is offline
 
I_Automation's Avatar
 
Join Date: Jun 2020
Location: Detroit, Michigan USA
Posts: 1,135
Quote:
Originally Posted by Snyd1 View Post
Most documents I have seen usually have a wiring diagram for single phase motors showing looped. If you are looking to save space, the Siemens SIRUS 3RM1 motors starters have overload protection and can save some serious space in a cabinet. They are 3 phase but here is an example of how they show to wire for single phase.

Your diagram is done a lot in the field, but I've never seen the 2nd phase wired reverse like your diagram shows.


Always looped to the top of the overload (or contactor/overload pair) and have the electricity flow downwards on all 3 contacts.


EDIT: Also it's quite common for the L3-T3 line to have the Neutral run through it and the hot looped through L1-T1 - L2-T2
__________________
ivanovaautomation.com


Some Jobs Are Best Started With A Sawzall And A Dumpster On Castors

Last edited by I_Automation; August 17th, 2022 at 03:31 PM.
  Reply With Quote
Old August 17th, 2022, 03:42 PM   #5
IanM8040
Member
United States

IanM8040 is offline
 
Join Date: Sep 2021
Location: omaha
Posts: 255
another example from rockwell

Capture.JPG
  Reply With Quote
Old August 17th, 2022, 04:10 PM   #6
Snyd1
Member
United States

Snyd1 is offline
 
Join Date: Jun 2018
Location: there
Posts: 217
Here is a FAQ specific to Schneider for the Tesys D series no pictures though only words

https://www.se.com/ca/en/faqs/FA117906/
  Reply With Quote
Old August 18th, 2022, 04:08 AM   #7
BryanG
Member
United Kingdom

BryanG is offline
 
Join Date: Feb 2005
Location: Manchester
Posts: 1,776
Three phase overloads have a function that checks for phase loss, so if you only put current through two legs, it trips. The 'normal' way of doing it in the UK is to loop the Line side through two legs and the Neutral through on the third leg. It works, no need to reinvent the wheel :-)
For very small motors it can sometimes be that the cost of the overload is greater than the cost of replacing a motor, so sometimes those are just fused/mcb'd to protect against short circuits. It depends on how important the motor is to the function of the machine and how easy it is to replace.
__________________
Knowledge is power, share the knowledge.
  Reply With Quote
Old August 19th, 2022, 03:27 AM   #8
jraef
Member
United States

jraef is offline
 
jraef's Avatar
 
Join Date: May 2006
Location: Northern California
Posts: 2,116
Before you go down that road further, make sure it is necessary. A lot of small single phase motors have built-in thermal OL protection inside of the motor. An external OL relay may be unnecessary.
  Reply With Quote
Old August 19th, 2022, 03:49 AM   #9
JesperMP
Lifetime Supporting Member + Moderator
Denmark

JesperMP is offline
 
JesperMP's Avatar
 
Join Date: Feb 2003
Location: ᚴᚬᛒᛅᚾᚼᚬᚠᚾ
Posts: 15,570
It is totally normal and the correct method to loop one phase through 2 contacts when you have a 2-phase motor.

Quote:
Originally Posted by BryanG View Post
Three phase overloads have a function that checks for phase loss, so if you only put current through two legs, it trips.
That is called "differential protection". It doesn't trip immediately when a phase is missing. The trip curve is slightly lower so that it will trip at a lower current value than if all 3 phases are present.

Quote:
Originally Posted by jraef View Post
Before you go down that road further, make sure it is necessary. A lot of small single phase motors have built-in thermal OL protection inside of the motor. An external OL relay may be unnecessary.
Do you mean that the overload protection is all internal, i.e. it cuts supply directly ? Or it is a potential-free N.C. that must be connected in series with the starting contactor ?
In the 1st case without a signal back to the motor starter, the control system will not know that the motor is not running which may be serious drawback.
In the 2nd case you need an additional cable, which may be a greater hassle than just using a normal overload.
OLs are cheap.
__________________
Jesper
NOTICE:
JesperMP can be impolite, has passive-aggressive tendencies and may use sarcasm !
Also: ᛁᚠ ᚢᚬᚢ ᚴᚬᚾ ᚱᛅᚬᛏ ᚦᛁᛋ ᚦᛅᚾ ᚢᚬᚢ ᚼᚬᚠᛅ ᚴᚬᛁᚾᛅᛏ ᛘᚢ ᚱᛅᛋᛒᛅᚴᛏ
  Reply With Quote
Old August 19th, 2022, 05:49 AM   #10
parky
Member
United Kingdom

parky is offline
 
parky's Avatar
 
Join Date: Oct 2004
Location: Midlands
Posts: 4,295
Agree with Jesper, TH O/L in the motor does not protect over current, examples are water in terminal box or a damaged cable so a trip before cable & motor is essential
  Reply With Quote
Old August 19th, 2022, 06:07 AM   #11
saultgeorge
Lifetime Supporting Member
United States

saultgeorge is offline
 
saultgeorge's Avatar
 
Join Date: Jul 2015
Location: Detroit
Posts: 525
I've definitely used the method of looping single phase through a 3-pole device. This also works well for DC devices, like a large DC motor on a wire draw machine for instance. Until one can install the proper breaker or device.
__________________
"Instant success teaches one nothing. Failure provides the tools and instructions one needs to succeed."
  Reply With Quote
Old August 19th, 2022, 10:41 AM   #12
I_Automation
Member
United States

I_Automation is offline
 
I_Automation's Avatar
 
Join Date: Jun 2020
Location: Detroit, Michigan USA
Posts: 1,135
Quote:
Originally Posted by jraef View Post
Before you go down that road further, make sure it is necessary. A lot of small single phase motors have built-in thermal OL protection inside of the motor. An external OL relay may be unnecessary.

I put them in when I want the PLC to know if the OL tripped.


If it's simply an internal protection that stops the motor the control wouldn't know the motor wasn't running anymore - or until it cooled down and restarted.



If it's a required process (a spray nozzle washing residue off a part so the next tank process isn't contaminated) then keeping the line running could be costly and create scrap.
__________________
ivanovaautomation.com


Some Jobs Are Best Started With A Sawzall And A Dumpster On Castors
  Reply With Quote
Old August 20th, 2022, 06:02 AM   #13
the_msp
Lifetime Supporting Member
United Kingdom

the_msp is online now
 
the_msp's Avatar
 
Join Date: May 2008
Location: Northern Ireland
Posts: 1,119
Thanks all. It's in the RFQ spec for contactor and overload, despite that yes, that costs more than the motor.
__________________
Regards,

Patrick G. B.Eng MIET

Making the flashy lights flash since the 90's

SCADA - Inductive Automation Gold Integrator | PLC | Control Panels | Robotics | Training

Connect with Matrix Engineering

My son was chewing on an electrical cord, so I had to ground him. He is doing better currently and conducting himself properly. My electrical skills are quite poor, which is a shock to some people
  Reply With Quote
Old August 20th, 2022, 05:11 PM   #14
jraef
Member
United States

jraef is offline
 
jraef's Avatar
 
Join Date: May 2006
Location: Northern California
Posts: 2,116
Ok. So if you buy a traditional NEMA design starter where the OL relay has replaceable heater elements it does NOT need to have power through all 3 phases. That issue only applies to IEC design overload relays. But a number of mfrs have taken to abandoning their older NEMA style OL relays because of changes in international rules on the materials used to make them, called “RoHS” (usually pronounced “Rohas”) that eliminated the use of lead solder. Those rules don’t apply to equipment being used in North America yet, so you can still buy the older NEMA type, just make sure it’s the type with replaceable heater elements instead of dual adjustable ones.
  Reply With Quote
Old August 20th, 2022, 07:53 PM   #15
I_Automation
Member
United States

I_Automation is offline
 
I_Automation's Avatar
 
Join Date: Jun 2020
Location: Detroit, Michigan USA
Posts: 1,135
Quote:
Originally Posted by jraef View Post
called “RoHS” (usually pronounced “Rohas”) that eliminated the use of lead solder. Those rules don’t apply to equipment being used in North America yet,

I worked in a circuit board shop that had many US customers specifying RoHS product, and not for export reasons, so it is coming here for no valid reason.


If you think about how much lead is in the solder on one circuit board, how many circuit boards could possibly be scrapped somewhere and how much lead would seep out of all of those there would be more lead naturally in the surrounding land.


Another rant: lead free solder on plumbing. The lead only leaches into stagnant water and would have to sit in a single pipe a few years to get a detectable level of lead and after all that time a person would have to drink gallons of it, then another house the next day.... Just to sell higher priced solder that doesn't work as good. Even the lead-free solder in the circuit board shop was difficult to work with, needed a higher temperature, harder to clean up after and created more waste that needed taken away and treated.
__________________
ivanovaautomation.com


Some Jobs Are Best Started With A Sawzall And A Dumpster On Castors
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
What materials do I need to wire a VFD to a three phase motor? belae1ka LIVE PLC Questions And Answers 17 December 14th, 2016 07:15 PM
Single Phase motor starter w OL protection? PLCRookie LIVE PLC Questions And Answers 5 July 6th, 2009 10:41 PM
what are the advantages for three phase power supply than single phase power supply ? magdyfayad LIVE PLC Questions And Answers 6 October 28th, 2008 03:42 PM
What do you call this voltage joeparrish LIVE PLC Questions And Answers 52 October 15th, 2008 03:20 AM
Mechanical/Material Handling and ISA 88 rlmunoz LIVE PLC Questions And Answers 6 December 25th, 2002 03:49 AM


All times are GMT -4. The time now is 03:26 PM.


.