1336F to Powerflex 700 on controlnet, PLC/5

Jasondelane

Lifetime Supporting Member
Join Date
Mar 2015
Location
Florence sc
Posts
221
Yesterday we had a 1336F pop and we don't have one in stock. We've got another one coming but in the meantime we're exploring the option of replacing it with a Powerflex 700.

I've put 20-Comm-c adapter on the powerflex and changed the node to the same as the old 1336F, and I can communicate with it via RSLinx, Drive Explorer, and RSNetworx. I've had no problem setting it up on RSNetworx, but for the life of me can't get the PLC to issue it a start or stop command using the same logic.

Looking through the program online, it seems that the PLC is not receiving a "drive enabled" status bit to allow it to send a start command.


Another thing is that when I go into the IO configuration on RSLogix 5, it's still showing a 1336 instead of a Powerflex after I've downloaded everything from RSNetworx and done a download from the PLC using the new Controlnet file.

I think I'm missing a step somewhere? Has anyone ever done this type of conversion?
 

Similar Topics

Hi all, I am working with an Allen Bradley 1336 Plus ii drive on an air compressor. We added a new pressure controller with a 4-20ma output and is...
Replies
2
Views
1,737
hi, I have the 1336f-L4 ac drive and somehow I cannot change/adjust value in program. The input mode alway in status even I plugin the TB3 module...
Replies
1
Views
1,347
Hello, I had to change old 1336F-brf20-ae-en to new same one. I recorded all parameters and put then into new drive. DeviceNet is not working...
Replies
2
Views
1,193
I've got a Powerflex 700 that doesn't like to get going in the mornings. This motor will run anywhere from 30 seconds to 5 minutes before it just...
Replies
3
Views
157
So I have a sort of unique situation where I'm wanting to run a PF755 from the IO and over ethernet. Of course, this comes with it's own set of...
Replies
9
Views
260
Back
Top Bottom