Cpu 414 Siemens resets sequentially ?!

sepehr

Member
Join Date
Dec 2008
Location
tehran
Posts
3
Hi all,
I have faced with a confusing problem, Dose anybody have a solution or comment?:confused:
In our plant we have about 30 set Siemens PLC (400 series) with relative modules (CP- I/O Cards - IM and etc... Connected via MPI and FDL networks)
From one week ago we have had problem with one of our plc station ( CPU 414-2XG02-0AB0 ) ; the memory of this CPU sequentially is resetting (fully) , we did all of fallowing actions but the problem still exist and these error codes are appearing in CPU diagnostic buffer ….
298d 0d00 0000 and 8002 0000 0000
Action1: we changed the CPU ….. and after 2 day , the problem appeared again.
Action2: we changed the Power supply ….. and after 1 day , the problem appeared again.
Action3: we changed the Rack (UR)….. and after 1 day , the problem appeared again.

For best explaining of this problem, I put the CPU "diagnostic buffer text" at the fallowing . please help and kindly guide me to solving this defection.
Many thanks

*** Diagnostic Buffer***

Event 15 of 120: Event ID 16# 430E
Memory reset executed
Initialization information: Memory reset due to inconsistent data
Previous operating mode: STOP (memory reset)
Requested operating mode: STOP (own initialization)
Incoming event
04:53:32:000 pm 01/13/09


Event 16 of 120: Event ID 16# 4309
Memory reset started automatically (power on not backed up )
Initialization information: Memory reset due to inconsistent data
No relevance for user (Z1): 0001
Previous operating mode: No voltage
Requested operating mode: STOP (memory reset)
Incoming event
04:53:32:000 pm 01/13/09


Event 17 of 120: Event ID 16# 4532
DEFECTIVE: failure of core resources
No relevance for user: 298d 0d00 0000
Previous operating mode: RUN
Requested operating mode: DEFECTIVE
Internal error, Incoming event
04:40:10:941 pm 01/13/09


Event 18 of 120: Event ID 16# 4535
DEFECTIVE: canceled by watchdog/processor exceptions
No relevance for user: 8002 0000 0000
Previous operating mode: RUN
Requested operating mode: DEFECTIVE
Internal error, Incoming event
04:40:10:940 pm 01/13/09
***
 
Hi Sepehr.

Since you have changed CPU, PSU and Rack, there only remains an external noise as the resaon for the CPU memory getting corrupted.
Start checking the obvious, grounding, screens, any new noise generating devices such as VFDs, commutators, coils without suppressors, flourescent lighting with a defective starter, etc.
 
i also faced same problem now, the s7 400 memory automatically reset every 2 - 3 hours. Does anyone solve the problem before?

Sepehr, are you still face the problem? any solution??

Thanks
 

Similar Topics

dear all experts one day i found that the master cpu's all leds is flashing and control transfered to the slave one after trouble shooting the...
Replies
1
Views
3,083
Hi Guys I have a problem with my siemens 414 PLC whenever we switch off or power goes it is not going in to RUN mode and we have to download the...
Replies
3
Views
3,185
Hello Team, I have an 6ES7414-3XM05-0AB0 CPU and someone wants to offer me 6ES7416-2XP07-0AB0 CPU as replacement part. I need to know if there are...
Replies
3
Views
1,953
Hi These questions are also created at Siemens network, but maybe there are more knowledge in here. :yeah...
Replies
2
Views
2,507
Hey all, I have been looking through the forums and many other places, and while I have found a lot of information, nothing seems to specifically...
Replies
5
Views
1,935
Back
Top Bottom