It will take a bigger gun to get that groundhog!4 hours ish.
thought of that. the problem is that I could have two of the three phases (the plug between the cars loses one), the detector would not turn on, which would trick the plc into thinking there's no power there, so it would then try to hook two sources together, which results in a rather spectacular light show. Don't ask me how I know that.
Another fun thing of this installation is that the ground power is 240 delta, while the generators are 240 y.
Each of the generator cars has a 120/208 transformer bank, while the cars downstream each has it's own 240/120 transformer. Makes load balance easier.
Anyway, is there any reason I can't use 240 volt relays across the phases? There's this wild phase that needs dealt with.
I have a son who is an EE, plus his boss, looking at this. Things were getting complicated.......
If its that critical - double them up per phase, so 6 relays in total and read all 6 inputs.
We've been known to use an elephant gun to shoot a groundhog around here.....
Is that a joke ?
Use the right tools for the right job:
https://www.tele-online.com/resources/data-sheets/en_e1pf400vsy01.pdf
Just make sure that when you are switching the power that everything is electrically and if required mechanically interlocked so you cant crash the two supplies should the PLC or the relays fail
I was thinking about using a phase relays, but there are situations where it will not activate,which would result in the plc trying to put two sources together.