Straight forward question from a Rockwell Newbie.
How do you configure a IP adress for the 1783-ETAP2F??
I'm only going to assign a IP adress to it and nothing more.
I have Rs logix micro and RSlinx lite.
I've downloaded the EDS file and installed it.
/Tim
A quick search suggests the manual
Rockwell Automation Publication ENET-AP005F-EN-P - October 2014, chapter 4, and it suggests the DIP switches have certain settings, depending on the required method.
Not had any experience of this, but did a quick google on the part number.
You can set the address can be set using BootP-DHCP tool that should have been installed when you installed Studio5000. This method works with most Rockwell products.
Ok, I have read the manual and I wanted to set the IP adress from the RSlinx as stated in the manual but I can't for my life figure out how.
I haven't got Studio5000 so I probably have to download the DHCP/BOOTP utility then
/Tim
I just set a couple of these up last month.
Step 1: Use the BOOTP/DHCP Tool to give them an IP address.
Step 2: Use the BOOTP/DHCP Tool or their profile in Studio 5000 to disable BOOTP/DHCP.
Step 3: Switch the DIP switches so they use the stored configuration (diagram in the Installation Instructions and on the side on the unit)
Step 4: Reboot and verify that the IP address is retained.
I am trying to connect to a Chiller through Modbus TCP that has been setup as a Modbus slave and I see the Rockwell AOI and it looks pretty...
410
Hello Mates, first time developing with deviceNet, Im more used with S7 CPUs. My system is a L23E CPU + PanelView 550 on devicenet. I can't...
788
Hi everybody. I got some problems about how to perform this task Now, I got an FB where I have this code snippet that looks like: L P##DBD_134...
1,147
Hello I got a request to make an exchange table using numeric addressing for a controllogix plc to talk with customer DCS (Delta V) I usually made...
2,399
Gents, I've not had much dealings with indirect addressing, but I'm troubleshooting a program now, and I just wanted to verify that I've come to...
3,013