PowerFlex 525 - Lobe Pump Flow PID Control

Hello,

I take part in commissioning of process station with lobe pump. Speed of the pump is controlled by PowerFlex 525. A customer requirement is to set a desired setpoint of flow for a pump. But there is no flow meter, there is only an encoder mounted on a shaft of a drive. Depending on a shaft gear ratio and pump efficiency (assumed that a dose per revolution is constant) I compute flow. To control this flow I want to use embeded PID control. Everything is cotrolled with PLC over Ethernet network so I set parameter A459 [PID 1 Ref Sel] to "Ethernet/IP" and parameter A460 [PID 1 Fdback Sel] as well. There is no problem with PID Reference signal - I can add parameter A464 [PID 1 Setpoint] to data structure and set it from PLC over Ethernet. But how can I connect actual value of flow computed in PLC to PID Feedback signal? I can't find this option anywhere.

I will be very thankful for any remarks.
  Reply With Quote
Old February 3rd, 2017, 07:54 AM   #2
rdrast
Lifetime Supporting Member
United States

rdrast is offline
 
rdrast's Avatar
 
Join Date: Apr 2003
Location: South Carolina Lowcountry
Posts: 5,307
This is for fluid?
A lobe pump for fluid generally has a fixed displacement per revolution, depending on the design and medium, it can be absolute or within a few percent so:

Flow = Rev's * Displacement
__________________
------------------------------------
How to ask questions the SMART Way!

Look First, Ask Second!

  Reply With Quote
Old February 3rd, 2017, 07:58 AM   #3
freju
Member
Poland

freju is offline
 
Join Date: Feb 2017
Location: Poland
Posts: 6
Thanks for your reply but you missedunderstood me. I know how to calculate flow and I do it in PLC so I have an actual value of flow. The problem is how to control this flow to obtain desired setpoint using embeded PID control in PowerFlex over Ethernet network.
  Reply With Quote
Old February 3rd, 2017, 08:04 AM   #4
Tom Jenkins
Lifetime Supporting Member
United States

Tom Jenkins is offline
 
Tom Jenkins's Avatar
 
Join Date: Apr 2002
Location: Milwaukee, WI
Posts: 5,921
You do not need or want a PID loop to control the flow of the pump. Simply back calculate the required rpm for the set flow rate, calculate the corresponding Hz, and send the command to the VFD. Done.
  Reply With Quote
Old February 3rd, 2017, 08:34 AM   #5
robertmee
Member
United States

robertmee is offline
 
robertmee's Avatar
 
Join Date: Feb 2008
Location: NC
Posts: 1,428
^ Agree....The 525 has it's own built in PID speed control. All you care about is that the 525 runs the speed (flow) you request. Since flow on a PD pump is proportional to speed, and you've already done the math, it's as simple as setting the speed SP for a given flow requirement.
  Reply With Quote
Old February 3rd, 2017, 09:47 AM   #6
rdrast
Lifetime Supporting Member
United States

rdrast is offline
 
rdrast's Avatar
 
Join Date: Apr 2003
Location: South Carolina Lowcountry
Posts: 5,307
Right. It is a constant displacement pump, so there is no need for a PID. Even if a mixing application, you just slave it to another component at a ratio, but your customer just wants to set X Gallons Per Minute or some such, no PID needed.
__________________
------------------------------------
How to ask questions the SMART Way!

Look First, Ask Second!

  Reply With Quote
Old February 7th, 2017, 05:38 AM   #7
freju
Member
Poland

freju is offline
 
Join Date: Feb 2017
Location: Poland
Posts: 6
Thank you for your remarks, you are right. For this purpose I don't need closed loop control - based on dependency between frequency and drive speed I will calculate appropriate frequency from flow setpoint.

But for future purposes - how can I connect value in PLC to PID feedback signal after setting parameter A460 [PID 1 Fdback Sel] to Ethernet/IP ?
  Reply With Quote
Old February 7th, 2017, 09:55 AM   #8
rupej
Member
United States

rupej is offline
 
Join Date: Sep 2014
Location: NC
Posts: 429
^If you have ethernet communications to a PLC, it would make more sense to do the PID in the PLC itself. That way you have much more control over everything.
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
AB ControlLogix PID control (gas pressure and flow - 2 valves) BGordon LIVE PLC Questions And Answers 4 May 1st, 2014 01:06 PM
PID loop control variable to powerflex 40 TheClint LIVE PLC Questions And Answers 3 March 31st, 2013 11:21 AM
PID Tuning for Flow. Any suggestions please? MorphuisOGrady LIVE PLC Questions And Answers 5 August 9th, 2010 04:14 PM
PID Control - Duty Assist pump niallbowie72 LIVE PLC Questions And Answers 21 July 24th, 2008 03:45 AM
Controlling flow using PID or other method? flyers LIVE PLC Questions And Answers 16 November 28th, 2006 03:54 AM


All times are GMT -5. The time now is 04:04 AM.


.