Why is this a thing? Why would you want 4mA representing 3277 engineering units, only to be scaled again for your process? Seems silly, I' sure I'm missing something important. For now, it is more of a hassle to try and wrap my head around the number changing three times before it represents your true value. Bleh
To have it make more sense to look at instantly.
4000 = 4.00mA, etc
If your scale is 0-100%, then at 90% reading that equals 18.4mA. If you see 18,400 on your intermediate scaled tag, then you instantly know 90%.
The analog to digital conversion is 14-bit resolution. The largest decimal number that can be represented in 14 bits is 16383. To put it another way, there are 2 to the power 14 combinations of 1's an 0's that can be made out of 14 bits. Those combinations represent the numbers zero (all 14 bits 0) through 16383 (all 14 bits 1).
The maximum decimal value represents the maximum analog signal, 20 mA. Zero mA is represented by a decimal value of zero. 4 mA is 20 percent of the way from zero to 20 mA, thus the decimal value corresponding to 4 mA is 20 percent of the way from zero to 16383, or 3277.
I have everything set up for vibration monitoring with the code in Controllogix 5000. The thing is that I am not able to read values SCADA in mm/s...
43
Hi, having some issues with scalings (SCP commands) with some Vegapuls 65 guided wave radar level transmitters. I've set the min/max in the...
235
I want to measure the tank level and get the sensor output to the PLC. Below are the details : Tank Height =0 - 3m, the sensor is stalled 0,2m...
740
463
I know nothing about simaticnet OPC server. I do know Kepware. I would only ever scale raw to engineering in the PLC, but it is possible to scale...
244