Good evening all. I have a Rockwell (AB) question for you all.

We recently added a rotary table to a machine for a customer. Mechanically this table can be physically removed from the machine when it's not needed. They want to be able to disconnect the motor & encoder cables when it's not in use & physically store the table away from the machine. The problem is that when the table is disconnected the other axes will not enable. When you try to enable them you get an error, "Axis Group Not Synchronized". If I remove the table from the Motion Group then it works fine, but when we reconnect the table it will not enable. When it's connected it needs to be part of the Motion Group since it needs to be in a coordinate system with several other axes.

Has anyone had any experience accomplishing this with Rockwell? I've done it with other control platforms.

Some facts:
  • CompactLogix
  • CPU = 1768-L45
  • Firmware = 19
  • SERCOS (Qty 2; 4-Axis cards)
  • Drives: 2094 style
 
Inhibit Axis Doesn't Work

My situation is baffling Rockwell support and two different distributors. The Inhibit Axis command does not work on my customers setup. I've come up with an alternative solution. The customer will press a button the HMI that will automatically download a different ACD file when he wants to add or remove this axis. It's crude, but it works.
 

Similar Topics

I have no experience with Eaton HMIs. I downloaded the Galileo software and I am trying to get the file on a HMI (XV-102-H3-70twrl-10) to modify a...
Replies
5
Views
117
How to fix if appears code “$115 plc-restart running” on the screen OP17
Replies
5
Views
247
Here's what happened, Operator turned on the disconnect for an auger while it was still running to cut power. Auger DID in fact turn off, but the...
Replies
8
Views
335
Hi! I am trying to run the 'SimpleSample' (https://infosys.beckhoff.com/content/1033/TF5100_TC3_NC_I/Resources/3438746891/.zip ) to understand the...
Replies
2
Views
104
A new point I/O rack is to be hooked up with the running PLC. In point I/O, it is supposed to be the OA4 card to be installed as per the...
Replies
1
Views
92
Back
Top Bottom