1762OF4 Analog Output
You can configure these modules for "Raw/Proportional" or for "Scaled for PID".
In "Raw/Proportional" mode the full scale output is a 16-bit signed integer, so +32767 counts = Full Scale Output.
The "Scaled for PID" means that they are scaled to take the full scale output of an SLC/MicroLogix PID instruction, which is 16383 for Full Scale Output.
Here's the tricky part, which is why there are a couple of Knowledgebase documents about it (38470 and 34193):
Full Scale is 10.5 volts (in Voltage mode) or 21 mA (in Current mode).
So even though the module is nominally a "0-10V DC" module, the full scale output value will actually generate 10.5 volts.
If you take into account the extra half-volt or extra milliampere, you'll get your best results.
The excerpt from the Knowledgebase that I always write down when I'm using these modules:
Code:
Raw/Proportional
Data Table Value   Voltage/Current Value
    32767                10.5 Volts
    31206                10   Volts
    0                     0   Volts
    32767                21 mA
    31206                20 mA
    6241                  4 mA
    0                     0 mA
Thanks Ken.
I'm using the Raw/Proportional and 4-20MA.
I'm not getting the correct mA from the card.
0 - 0% - 0mA
8191 - 25% - 5.2mA
16838 - 50% - 10.5mA
24575 - 75% - 15mA
32767 - 100% - 20mA
Thanks Ken.
0 - 0% - 0mA
8191 - 25% - 5.2mA
24575 - 75% - 15mA
32767 - 100% - 20mA
See chart below
Remember 0 counts (raw data) = 0ma 0%
32767 counts (raw data) = 21ma 100%
If you are looking for % of 4-20ma then see chart 2
6242 counts (raw data) = 4ma 0% 0f 4-20ma
31206 counts (raw data) =20ma 100% of 4-20ma
Does the 1762-OF4 card require a Position Feedback to operate?
The reason I'm asking, I having a issue moving a actuated valve with this output card but I can move the valve with a 789 process meter.
If I source the valve and give it 12mA the valve will move half way.
So I thought it may be in the wiring of the PLC card.
Thanks again for your help
It may be in the wiring to the card. After a quick look at the manual for that card it looks like you have to make sure you are connecting to an amperage output and not a voltage output.
Bubba.
Hi all. I have 1793-IE4 (4)analog inputs modules in a 1794-ADN IOFlex DeviceNet Rack. I cannot find if I can I have access to individual channel...
49
Good afternoon, I am currently working with an HMI/PLC LP-a070 and I require at least one analog output, but the PLC does not have one. I was...
140
Hi all. Customer wants analog faceplates really bad, even if we explained that it doesn't make much sense in his process. What he wants to see...
144
I'm having trouble calming down 2 Tempo Sonics. I'm using Studio 5000 CompactLogix my Raw value is jumping around from 8575.0 to 8755.0 at a...
30
1,217
294