plc storereviewsdownloads
PLC training tools sale
Reply
Thread Tools Display Modes
Unread December 10th, 2019, 01:29 PM   #1
Lucask
Denmark
Lucask is offline
Structured text
I'm trying to get some good habits regarding structured text.
So that's why I'm looking for some info from others with experience in that area.
I've added a small program where the same output is controlled in each step (or where it is needed)
Would you handle it like this.
Case Istate of
0:
Motor1:=FALSE;
IF Statement_1 then
Istate:=10;
END_IF
10:
Motor1:=TRUE;
IF Statement_2 then
Istate:=20;
END_IF
20:
Motor1:=FALSE;
IF Statement_3 then
Istate:=30;
END_IF
30:
Motor1:=TRUE;
And so on...
End_Case
Or more like when making a Ladder program, where the output is only set one place, and then controlled by the steps.
Like this:
If Istate = 10 OR Istate = 30 then
Motor1:=TRUE;
ELSE Motor1:=FALSE;
Thanks!
Unread December 10th, 2019, 02:12 PM   #2
AustralIan
Germany
AustralIan is offline
1st way is easier to follow the sequence.
2nd way is easier to trace back an output.
Be consistent.
I prefer the second way.
But your if else statement is better as:
Motor1 := ( Istate = 10 ) OR ( Istate = 30 ) ;
Also, if your controller supports ENUM you should definitely use them instead of numbers.
Unread December 10th, 2019, 02:14 PM   #3
Jobbe9000
Denmark
Jobbe9000 is offline
Well..... Both ways will work.
Personally i prefer the first way you do it.
In case you had 50 steps where you would set Motor1 to true, the if statement would be quite a hassle to look at.
Both ways will work fine though.
Some people will tell you to be consistent with the way you choose.. some people will tell you to use the best way suited in the specific case.
Instead of choosing which of the 2 ways to do it, I would focus more on your layout of the code.
1: Use indentation
IF bStatement1 THEN
bOutput1 := TRUE;
ELSE
bOutput1 := FALSE;
END_IF;
2: Keep Keywords in either lower case or UPPER case
3: Keep consistent naming of your tags.
In the example code your example you use prefix Istate and not on Statement_1
In my case iState looks more readable to me.... but that is because i use lower camel case tag naming myself.
4: Use constants for state names in your case statement, instead of 10, use a constant with a value of 10. This makes it easier to read, and you wont end up having to change "10" a thousand places in case you end up needing to change the state number.
5: Use a have a init or reset step, where all tags set in the statemachine is reset to their initial values.
Take a look at PlcOpen's programming guidelines.
It is really good reading.
Unread December 10th, 2019, 02:35 PM   #4
Engineer_MG
United States
Engineer_MG is offline
Engineer_MG's Avatar
For simple boolean control the second way is better.
I use CASE for complicated sequences, benefits
1. You can store last active step (good for debugging in a sequence and restarting conditions)
2. Jump to a defined step when there is a global alarm
etc.
Sample as below ( I copied this from my PLC code so the formatting is messed up in this page):
IF g_xMachineAlarm THEN
g_iSequencer := 999;
END_IF
CASE g_iSequencer OF
0: // Wait for Run execute
g_iLastSequencerStep := 0;
IF g_xRunExecute THEN
g_istepNumExe := 1; // Always start from 1
g_iSequencer := 10;
END_IF
10: // Store current step of the program
g_iLastSequencerStep := 10;
g_iCurrentActiveStep := g_iStepNumExe;
g_iSequencer := 20;
20: // Check Jump
g_iLastSequencerStep := 20;
IF PRg_array[0].astSteps[g_iCurrentActiveStep].iJmpInt > 1 THEN // Jump active
g_iJmpFromStep := g_iCurrentActiveStep;
g_iJmpToStep := Prg_Array[0].astSteps[g_iCurrentActiveStep].iJmpInt;
g_dwCurrentJmpRepCtr := Prg_Array[0].astSteps[g_iJmpFromStep].iRep;
g_xJumpActive := TRUE;
g_iSequencer := 180;
ELSIF PRg_array[0].astSteps[g_iCurrentActiveStep].iJmpInt = 1 THEN
g_xJumpActive := FALSE; // Program end
g_iSequencer := 600;
ELSIF PRg_array[0].astSteps[g_iCurrentActiveStep].iJmpInt = 0 THEN // No Jump , timer disable if rep > 1, timer enable = rep =1
g_dwCurrentRepCtr := Prg_Array[0].astSteps[g_iCurrentActiveStep].iRep;
g_iSequencer := 30;
END_IF
30: // No Jump , Solenoids activation, activate timer for the first time for step changeover and then disable
g_iLastSequencerStep := 30;
g_xCallSolenoidExecute := TRUE;
g_iSequencer := 35;
999: // Alarm active, resets
END_CASE
Thanks.
Quote:
Originally Posted by Lucask View Post
Case Istate of
0:
Motor1:=FALSE;
IF Statement_1 then
Istate:=10;
END_IF
10:
Motor1:=TRUE;
IF Statement_2 then
Istate:=20;
END_IF
20:
Motor1:=FALSE;
IF Statement_3 then
Istate:=30;
END_IF
30:
Motor1:=TRUE;
And so on...
End_Case
Like this:
Motor1:=TRUE;
ELSE Motor1:=FALSE;
Thanks!
Unread December 10th, 2019, 03:53 PM   #5
busarider29
United States
busarider29 is offline
I tend to do it your first way in ST, especially if I have several variables that need to be set to different states throughout the CASE steps. It's just easier from a programming standpoint and also when stepping through the CASE for debugging.
I know setting something to TRUE/FALSE should be done in one place, like in LD, but from my experience, it's not always very practical in ST.
Unread December 10th, 2019, 04:59 PM   #6
James Mcquade
United States
James Mcquade is offline
Welcome to the forum.
I am not sure what your application will be, but; please remember who your end user is when programming a plc. It is maintenance. you need to know what their capabilities are in regards to programming and what they are used to.
james
Unread December 10th, 2019, 05:39 PM   #7
CapinWinky
United States
CapinWinky is offline
CapinWinky's Avatar
I've done a lot of state machines for a lot of different kinds of machines and processes. I've settled on setting/unsetting statuses and outputs in each state. I also check in each state if the command that got me in there is still active and if not, I bail back out to the wait state. This does make each of my states have some copied lines in overhead, but it provides maximum flexibility and readability, which has proven more important on a regular basis.
Setting outputs at the end of the state machine based on the active state is simply too hard to follow when state machines get large and it inevitably requires additional conditions besides just the state number if reaction time is a factor. There is a way around the reaction time issue that is fairly clever, but I don't particularly like it. Here is an example (I don't do this):
20..25: //This state code will work for states 20 to 25
<Some Code>
IF(MyCondition) Then
MyState:=21;
END_IF
<SomeCode>
MyOutput:= (MyState=5) OR (MyState=21);
This lets you turn on the output the same scan your condition is true instead of waiting a scan to go the next state.
Instead, I just do stuff like this:
20: //Wait to do the thing state
StatusDoingThing:= 0;
IF(DoTheThing) Then
MyState:= 25;
TheThing.DoIt:= 1;
END_IF
25: //Do the thing
StatusDoingThing:= 1;
IF(NOT(DoTheThing)) Then
MyState:= 0;
TheThing.DoIt:= 0;
ELSE
IF(TheThing.NextStepReady) Then
TheThing.DoNextThing:= 1
MyState:= 30;
END_IF
END_IF
etc...
__________________
Cycling power is a sign of weakness.
Unread December 10th, 2019, 06:41 PM   #8
janner_10
United Kingdom
janner_10 is offline
Use it when it's easier to, use ladder when it's easier to.
Don't be obsessed with using ST when ladder could be better.
Also Comments Comments Comments
Unread December 11th, 2019, 03:37 AM   #9
cardosocea
United Kingdom
cardosocea is offline
This is the correct answer...
Unread December 11th, 2019, 06:23 AM   #10
LadderLogic
United States
LadderLogic is offline
LadderLogic's Avatar
The opposite is true too
__________________
Don't trust, don't fear, don't beg...
Unread December 11th, 2019, 07:12 AM   #11
ndzied1
United States
ndzied1 is offline
ndzied1's Avatar
For state machines I have found it very useful to define a string variable and update it for each state with the "name" of the state. For sure it's useful when debugging and also could be brought out to an HMI for describing the sequence to the operator.
I put it on the same line as the number or constant defining the start of the step and it usually takes the place of a comment I would have put there anyway.
Code:
iState: INT;
sStateName: STRING;
CASE iState OF
   0: sStateName := 'Waiting for Start';
   1: sStateName := 'Down @ Pickup, Gripper Open';
   2: sStateName := 'Close Griper @ Pickup';
   3: sStateName := 'Raise @ Pickup, Gripper Closed';
   4: sStateName := 'Extend to Drop-off';
   5: sStateName := 'Lower @ Drop-off';
END_CASE
__________________
nOrM
nOrM=Norman Dziedzic Jr.
I've never been to China but my phone has.
Unread December 11th, 2019, 07:25 AM   #12
ndzied1
United States
ndzied1 is offline
ndzied1's Avatar
You can write an entire IF/THEN statement on a single line if the conditions are short and it makes sense. It can sometimes encapsulate the idea of what you are trying to do in a cleaner fashion than 3 separate lines. BUT, it's not for everything.
Here are lines doing an analog conversion for some flow meters. Vibration on the machine means that when there is no flow, the pickups still get some signal and show a very small flow. Forcing these small values to zero does not effect the process and makes the HMI clearer for the operators.
Code:
InputFlow[0]     := AnalogConversion(FM3,20000,4000,15.85,0.0);
IF InputFlow[0]  < MIN_FLOW THEN InputFlow[0]  := 0.0; END_IF;
OutputFlow[0]    := AnalogConversion(FM4,20000,4000,15.85,0.0);
IF OutputFlow[0] < MIN_FLOW THEN OutputFlow[0] := 0.0; END_IF;
InputFlow[1]     := AnalogConversion(FM1,20000,4000,15.85,0.0);
IF InputFlow[1]  < MIN_FLOW THEN InputFlow[1]  := 0.0; END_IF;
OutputFlow[1]    := AnalogConversion(FM2,20000,4000,15.85,0.0);
IF OutputFlow[1] < MIN_FLOW THEN OutputFlow[1] := 0.0; END_IF;
__________________
nOrM
Unread December 11th, 2019, 09:01 AM   #13
theColonel26
United States
theColonel26 is offline
theColonel26's Avatar
Be consistent.
Yes be Consistent
ENUM +1000
1: Use indentation
IF bStatement1 THEN
bOutput1 := TRUE;
ELSE
bOutput1 := FALSE;
END_IF;
james
Wrong, this kind of mind set is how we end up with such terribly written PLC code in the US. You should write code for other competent PLC programmers to understand. That doesn't mean make an inconsistent mess with a whole lot of "clever" logic, but it does mean take full advantage of the Programming tools that the environment provides you and try to maintain good DRY (Don't Repeat Yourself) and SOC (Separation of Concerns) practices. I see so much code that is written by Controls "Engineers" that is a giant knot of spaghetti with glue sauce, when I try to explain DRY and SOC practices to them I might as well be speaking Klingon. Anything other than Copy/Paste throw a NO there, put a NC there is to scary to try to grasp.
I'm not a degree-ed Engineer (no BS in Engineering that is), but I do consider myself to be an engineer. Engineering is a mind set and a way of thinking. I have encounters controls engineers that have real Engineering Degrees and I don't consider them engineers because they create messes.
This topic may need it's own thread.
Yes
Quote:
and yes
Quote:
IMO that makes it harder to read, especially if you go back and forth between styles in the same project.
Unread December 11th, 2019, 09:35 AM   #14
busarider29
United States
Quote:
With the risk of high-jacking this thread, I whole-heartily agree with the above. Take advantage of the tools that are provided, including the programming languages. Use the language that is best for the routine you're coding.
"Keep the maintenance people in mind when writing PLC code" is essentially implying to write it all in LD so the maintenance people can understand. If one cannot understand IF_THEN_ELSE, then that person should be nowhere near the PLC in my opinion. It's written in plain English (IF_THEN_ELSE). How much easier does it need to be? Okay, so you might have to learn what a CASE statement is and a FOR loop. No different than the numerous instructions outside of a XIC, XIO, and OTE in a RSLogix ladder program that one had to learn!
Unread December 11th, 2019, 10:03 AM   #15
ndzied1
United States
ndzied1 is offline
ndzied1's Avatar
Stylistic choice I guess. As I said, it's not for everything.
__________________
nOrM
Reply
Bookmarks
Thread Tools
Display Modes
Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts
BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump
MSG Instruction via Structured Text jfd7851 LIVE PLC Questions And Answers 5 August 10th, 2016 11:15 AM
Structured text in factorytalk view studio? Crailberry LIVE PLC Questions And Answers 1 July 2nd, 2016 04:05 PM
Structured Text & RSLogix - good reference books & docs? ChrisOfMaryland LIVE PLC Questions And Answers 4 November 4th, 2009 01:10 PM
Structured Text for automating experiments? I'm new... ChrisOfMaryland LIVE PLC Questions And Answers 1 November 4th, 2009 12:40 PM
Documentation on Structured Text cmulder LIVE PLC Questions And Answers 13 June 11th, 2003 11:10 AM