I have been tasked with a lot of cicode, i'm an electrician so its not my strong point but i am coping.

anyway my questions are simple for someone with experience.

Q1

i just need to know the correct syntax for passing a substitution string to a super genie, i am getting association errors.

i want to pass the string sFiberiser(variable) to the super genie in place of "'D2 Fiberiser 4'" the code works as i do get D2 Fiberiser 4 displayed on the super genie,its just not a variable

FUNCTION
Oldest_Spinner(STRING sTagbase)

INT bOldSpin; ! Check on commissioning
STRING sFiberiser = sTagbase; ! sTagbase is Passed from another function

AssWin("!DevFibSpinAge",250,300,8+64+128+256+1024, sTagBase+"_SPIN_HRS", sTagBase+"_SPIN_ID", "'D2 Fiberiser 4'",
"bOldSpin", sTagBase+"", sTagBase+"", sTagBase+"", sTagBase+"");

WinTitle("D1 Spinner Excessive Hours !");

END


Q2

With the following Function i am trying to totalisea flow rateof molten glass.

the Real World tag "FH_Z302_PVM" from instrumentation is the Pull Rate (The flow rate) of the glass in kG/Min typically 10.0kg per minute.

so i run a continuous task every minute via "while True do" function and before it loops i use "Sleep(60)" pause for 60 seconds.

if the boolen tag bD1Fib1Prod = 1 it is to start totalising (in production) this works well

my question is does this concept look right?

FUNCTION
Spinner_Pull_Rate()

// Start Values of D1 Pull rates
REAL D1_1GlassPull_Str;

// Average Values of D1 Pull rates
REAL D1_1GlassPull_Avg;
;

// Totalised Values of D1 & D2 Pull rates
REAL D1_1GlassPull_Tot;


// Booleen tags for Position "Production Status"
INT bD1Fib1Prod ! D1 Fiberiser 1 is in Production


WHILE True DO ! Continuous Loop (every 60 Seconds)

! *********** D1 Positions in Production **********************************************************

! if Cullet Chute Out AND Spinner Running AND Glass > 900 THEN D1Fib1 is in production.
IF CW_D1F1CH_OUT = 1 AND FM_D1FIB1_RUN = 1 AND FH_Z302_PV > 900 THEN bD1Fib1Prod = 1;
ELSE
bD1Fib1Prod = 0;
END;

! *********** D1 Production Glass Totalising **********************************************************

! D1Fib1 is in Production - Totalise the Spinner Pull
IF bD1Fib1Prod = 1 THEN

D1_1GlassPull_Avg = ((D1_1GlassPull_Str + FH_Z302_PVM) / 2); ! Average the pull over 1 Minute (the pull at start of minute + Pull at End of minute / 2)
D1_1GlassPull_Tot = (D1_1GlassPull_Tot + D1_1GlassPull_Avg); ! totalise by adding the last value with new value "every minute"


END ! IF Statement end

Sleep(60); ! Run Every 60 Seconds

FM_D1FIB1_SPIN_TONNES = (D1_1GlassPull_Tot / 1000); ! Convert kG to Tonnes

! *********** Capture the "Start of Minute" Values of all Positions **********************************************************

D1_1GlassPull_Str = FH_Z302_PVM; ! D1 # 1 Glass Pull Rate Instantaneous Value (Start of Minute Value)


END ! WHILE True DO end

END
 
Q1, you want to pass the value and not the tag name so you would do this.

AssWin("!DevFibSpinAge",250,300,8+64+128+256+1024, sTagBase+"_SPIN_HRS", sTagBase+"_SPIN_ID", "'" + sFiberiser + "'","bOldSpin");


Q2, Your bD1Fib1Prod flag is not really useful and just double handling. I would just delete it and replace it with your calc like below. Also the value of D1_1GlassPull_Tot will retain last value when condition is not true (not in production).

Code:
	IF CW_D1F1CH_OUT = 1 AND FM_D1FIB1_RUN = 1 AND FH_Z302_PV > 900 THEN 
		D1_1GlassPull_Avg = ((D1_1GlassPull_Str + FH_Z302_PVM) / 2); ! Average the pull over 1 Minute (the pull at start of minute + Pull at End of minute / 2)
		D1_1GlassPull_Tot = (D1_1GlassPull_Tot + D1_1GlassPull_Avg); ! totalise by adding the last value with new value "every minute"
	END;

With this calc after the sleep, would you not want to do this straight away and have it before the sleep function?
FM_D1FIB1_SPIN_TONNES = (D1_1GlassPull_Tot / 1000);
 
Hi Andrew,


thanks for your reply i tried the syntax "'" + sFiberiser + "'" and its exactly what i wanted. i spent way too long on this simple task yesterday, many thanks.



much appreciated. will work on your suggestion to question 2 today
 

Similar Topics

Hello, the system we use is Scada 7.5 series. We have usb key activ now we need additional key to make the system work, how do we solve this...
Replies
0
Views
68
So i've been at this for a long while, i have Citect Scada 2018, i have full access to everything but i can't seem to find any option or...
Replies
0
Views
78
I am trying to display a variable within a cicode function onto a graphics page. This function queries a SQL database. I can get the value onto a...
Replies
3
Views
330
We are trying to set up a newer generation Omron PLC (NX/NS Series) with Citect / Aveva Plant SCADA using the Ethernet/IP CIP Protocol to read...
Replies
2
Views
417
I am new to Citect SCADA and I am building the graphics for a page that will contain the control of a plant by a Kingfisher RTU. The project I...
Replies
0
Views
289
Back
Top Bottom