PID control of differential pressure across a control valve

Second guessing myself here, need someone to either tell me I'm wrong or confirm that my thinking is correct please.

I have an equal-percentage characteristic control valve and I need to control differential pressure across it. This is a secondary control mode. The primary mode is control based on flow rate (equal-percentage -> linear installed characteristic, so flow rate is linear with valve position, ideal for PID). When I have to do dP control, PV should be the square root of dP, correct? Because dP is proportional to flow rate squared, so I should sqrt dP in order for it to work with a PID loop properly.
__________________
Quote:
Originally Posted by ganutenator View Post
customers:
I don't know how to do it so it must be easy
  Reply With Quote
Old March 20th, 2017, 04:35 PM   #2
Tom Jenkins
Lifetime Supporting Member
United States

Tom Jenkins is offline
 
Tom Jenkins's Avatar
 
Join Date: Apr 2002
Location: Milwaukee, WI
Posts: 5,710
If you are trying to use a valve as both control device and flow meter you will probably have poor results.

If you are trying to control both flow and differential pressure you will definitely have poor results.

Look at the equations here: http://www.engineeringtoolbox.com/fl...nts-d_277.html

For a given valve position Cv is fixed. But, unless your upstream pressure is a constant, the flow for a given valve position isn't fixed. You can have many flow rates for a given valve position as the upstream pressure varies.

If you want to control flow you should use a flow meter, and use your control loop to vary valve position until you get the flow you need.
  Reply With Quote
Old March 20th, 2017, 04:40 PM   #3
Epy
Lifetime Supporting Member
United States

Epy is offline
 
Epy's Avatar
 
Join Date: Jul 2012
Location: Allen-Bradley Valley
Posts: 265
Was about to come and post to disregard, stress-related brainfart. Thanks for replying though Tom.

There is a flow meter. Primary control mode is based on flow rate from flow meter, changing valve position to control flow rate. Secondary control mode is differential pressure control based on upstream/downstream pressure transducers. Won't be doing both modes at the same time, one or the other. Will use the square root of dP as PV for the secondary mode.
__________________
Quote:
Originally Posted by ganutenator View Post
customers:
I don't know how to do it so it must be easy
  Reply With Quote
Old March 20th, 2017, 05:11 PM   #4
mellis
Member
United States

mellis is offline
 
Join Date: Nov 2004
Location: Cincinnati, Ohio
Posts: 757
Just a comment...

Equal percentage characteristic is based on the pressure drop across the valve NOT being constant. It achieves a near linear installed characteristic only if the pressure at low opening is much higher than at full opening. If you control the pressure across an equal percentage valve, then the installed flow characteristic becomes parabolic.
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
allen bradley PIDE proportional vs derivative rollex LIVE PLC Questions And Answers 25 January 27th, 2016 09:06 AM
PID valve control valahia@gmail.com LIVE PLC Questions And Answers 2 April 15th, 2012 01:45 PM
RS5000 PID Instruction Assistance knight1fox3 LIVE PLC Questions And Answers 27 June 10th, 2010 04:41 PM
[S7] PID control between control valve and load cell ascoldasice LIVE PLC Questions And Answers 4 July 20th, 2006 10:42 AM
Proportional-only control – why won’t it work right? Ron Beaufort LIVE PLC Questions And Answers 13 April 25th, 2005 04:18 AM


All times are GMT -5. The time now is 09:34 AM.


.