ProFace HMI to Mitsubishi PLC
Hello Everyone,
I am hoping someone can point me in the right direction. I have a Mitsubishi PLC FX3u connected to an old ProFace GP2500 HMI Ver4.35 via serial. The HMI tag for a "Keypad Input Display Setting" data entry box is LS0206 See attached image. Can anybody assist with where this tag will write to within the PLC? Thank you Woolie
__________________
----------------------------------------------------------- You are only young once but you can stay immature forever! |
![]() |
![]() |
#2 |
Member
|
Its not, LS bits are local internal bits/words so probably not used or are used internally in some sort of script or function.
The chances are the original programmer used the default [PLC1]Dxxxx etc. for the PLC addresses. |
![]() |
![]() |
#3 |
Lifetime Supporting Member
![]() ![]() Join Date: Aug 2012
Location: Eltham
Posts: 65
|
Thanks Parky,
That makes a lot more sense. Although I haven't found any scripting within the project, I have found a page buried deep that uses a "D" register for the input value. This project has over 60 pages, but from what I can see only 8 are accessible to the Operators. Go Figure!!! Once again, thank you for share your knowledge. Woolie
__________________
----------------------------------------------------------- You are only young once but you can stay immature forever! |
![]() |
![]() |
#4 |
Member
|
It is often the case, there is probably no need to reference the keyboard in the PLC, the variable you are editing is the only thing that needs data, the edit field automatically calls the keyboard.
I'm not sure why the PLC needs to know but it's that long ago since I did any proface. |
![]() |
![]() |
#5 |
Member
![]() ![]() Join Date: Apr 2016
Location: From Canada - Living in Bulgaria
Posts: 1,948
|
Just to share, I had a project that did exactly this - all the screens had LS data, and there was a script to copy all the data back and forth to the PLC.
__________________
Automation Programmer PLC / HMI / SCADA / SQL New Systems, Modifications System Upgrades & Conversions Siemens EPROM & EEPROM Service ------------------------ Visit: contrologica.com Email: info@contrologica.com |
![]() |
![]() |
Currently Active Users Viewing This Thread: 1 (0 members and 1 guests) | |
Thread Tools | |
Display Modes | |
|
|
![]() |
||||
Thread | Thread Starter | Forum | Replies | Last Post |
Problem connecting Weintek HMI to PLC using Modbus TCP/IP | TahirQ | LIVE PLC Questions And Answers | 9 | September 9th, 2020 10:32 PM |
Connect Q02H PLC to HMI Proface | anhtuandrg | LIVE PLC Questions And Answers | 0 | January 29th, 2016 04:22 AM |
AB hmi with Mitsubishi Qseries PLC? | Rajasekar.P | LIVE PLC Questions And Answers | 4 | September 23rd, 2013 12:49 PM |
GT1020-LBL to Keyence PLC (Mitsubishi HMI to PLC other brands) | Andreik | LIVE PLC Questions And Answers | 1 | June 14th, 2012 10:28 PM |
Disconnecting HMI and connecting PC to Mitsubishi PLC (A-series) | mkac | LIVE PLC Questions And Answers | 4 | June 17th, 2010 05:25 AM |