Hey all,
Im looking for a little clarity on the ONS instruction
When taking a pump from auto to manual, I would like a bumpless transition. So I am moving an automatic pid cv in to the pumps power output, when manual control has been selected.
Im doing this with a ONS instruction, and from there the manual sp can be played with.
If I put the pump back into auto, and then again back into manual that ONS instruction will not move the CV into the manual sp again.
I was under the assumption that if the rung the ons instruction is on becomes false and then true again it should function on the next scan?
Can anyone help me with a way to assure that this will function as intended in the event of toggling like as mentioned above?
Thanks so much for your help.