question about logix 500 ONS instruction.
Shiro485
Apr 2013
North Haven CT
103
Hey all,
Im looking for a little clarity on the ONS instruction
When taking a pump from auto to manual, I would like a bumpless transition. So I am moving an automatic pid cv in to the pumps power output, when manual control has been selected.
Im doing this with a ONS instruction, and from there the manual sp can be played with.
If I put the pump back into auto, and then again back into manual that ONS instruction will not move the CV into the manual sp again.
I was under the assumption that if the rung the ons instruction is on becomes false and then true again it should function on the next scan?
Can anyone help me with a way to assure that this will function as intended in the event of toggling like as mentioned above?
Thanks so much for your help. :D
I suspect you are referencing the ONS storage bit in multiple locations. The storage bit may be used only once.
Are you using the PID A/M bit? For bumpless transfer set the PID A/M bit and then write directly to the CV.
It would help if you told us what processor you are using and post your code ( .RSS file) zip it first if you can.
The PID instruction is also different depending on the processor you have.
I added T4:50 to delay the OTE from coming on, but the customer only wants T4:50 to delay the OTE every 12 hours. I am a beginner and can't...
2,809
The customer that this machine is being built for has requested I add more pre loaded samples to this program. Just to review, I'm using RS Logix...
2,644
Hi all, I'm using a Micrologix 1400 PLC. I have 8 physical DI's, 4 DO, 4 AI's that will be radio transmitted to a DCS Master. The DCS is a Bailey...
9,435
We recently had an issue with one of our systems. I was trying to trouble shoot from RsLogix, however I dont have the original logic file, so...
1,292
I've done a few AB projects, but have not seen either of the following in a MOV instruction (I can't figure how to take a "snippet" and insert). I...
3,293