ASCII code for Micrologix 1100

Hi Guys, i am reposting this beacuse I'm still having issues with the "READ" ARL or ARD instructions. I have a pdf of a program that I found on the Rockwell site that is slightly modified for the Write command but I can write fine. I would like to be able to read back commands that I just wrote to the device as well as solely just monitor certain ASCII data from the device. Cannot seem to read any ASCII from the device and not sure how to set up my string table for the reads. Any help would be much appreciated.


Hello, I am working with a micrologix 1100 allen bradley plc and I need to send and receive ascii code to a sensor device. The syntax for the commands that the manufacture states are the following:

set:LO=xxxx -(to set the low speed)
set:HI=xxxx -(to set the high speed)
I can get this to work using an AWA write command with a ACN command by typing the (set:LO=) in my ST string file and loading the xxxx variable from an hmi into and interger file and using an AIC command.
it works pretty well.

What I am having problems with is how to read information from the sensor.

get:LO=xxxx
get:HI=xxxx...


I am not certain how I can read these with and ARL or ARD instruction.. Or do i need to do something else. I will also need to convert it back to an integer file.

Thank you for your time!!!

Steve
Attached Files
File Type: pdf 1763_ML1100_ASCII_WRITE_READ 4 plc talk.pdf (19.0 KB, 18 views)
  Reply With Quote
Old March 15th, 2019, 10:30 AM   #2
OkiePC
Lifetime Supporting Member
United States

OkiePC is offline
 
OkiePC's Avatar
 
Join Date: Mar 2005
Location: ENE of Nowhere Oklahoma
Posts: 10,131
At first glance, it still looks a bit too simple to cover all your bases. It has been over ten years since I had to to ASCII with ladder logic, but when I did, I ended up with a state logic control over the steps and several places where I had my own timeouts and recover branches. I don't have access to that code or enough memory of the details to say much more.
__________________
It's not all the variables I am most concerned with, it's the undiscovered constants.
  Reply With Quote
Old March 18th, 2019, 06:38 AM   #3
sellis4003
Member
United States

sellis4003 is offline
 
Join Date: Feb 2019
Location: maryland
Posts: 6
Thanks for the reply Okie. Yes this is know this is too simple for what I am trying to do. I had some more complex code written with different time delays and more ASCII values that I needed to write and read but reverted back to this because I wasn't able to read anything back at all and thought I should start simple. I found this example on the Allen Bradley Website and Added the AIC and ACN for the write since I need to load the values from a touch screen. The writes all seem to work fine. I'm thinking it has something to do with the SYNTAX that the ASCII device is looking for. When I do a Write, I have to type a (set:LO=) into my string data file but not sure how to handle this for a read since the device is looking for a (get: LO=) to read a value. Any help would be much appreciated... Thanks again Steve!!!
  Reply With Quote
Old March 18th, 2019, 03:50 PM   #4
shawn_75
Member
United States

shawn_75 is offline
 
Join Date: Apr 2010
Location: KY
Posts: 365
I think your scan time is beating out the very slow speed of the ARD. I'd separate out your AEX and ACI from the ARD. Use the ARD /DN bit to trigger the AEX and ACI.

Edit: I see that you need to write a get: command, then the device will respond with the value you want. If this is the case, I'd try to first clear the buffers, AWT your get: command, then test the buffer, then read. Give your AWT and ARD time to do their work as they can be quite slow. Trigger any concatenation off their /DN bits.

Last edited by shawn_75; March 18th, 2019 at 04:01 PM.
  Reply With Quote
Old March 19th, 2019, 06:13 AM   #5
sellis4003
Member
United States

sellis4003 is offline
 
Join Date: Feb 2019
Location: maryland
Posts: 6
Thank you Shawn for the quick reply. I appreciate your input, it certainly make a lot of sense. I was wondering if I had to do an AWT for the get as well. I will give these things a try and keep you posted.. Thanks again, Steve
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
ASCII code for Micrologix 1100 sellis4003 LIVE PLC Questions And Answers 3 March 14th, 2019 07:28 AM
PLC5 and Factory talk view studio 7 jasonm LIVE PLC Questions And Answers 12 October 15th, 2014 04:19 PM
Micrologix 1100, ascii string, ethernet, rs232 lloydsteve LIVE PLC Questions And Answers 1 April 17th, 2009 11:37 PM
Micrologix 1100 ASCII out to Zebra Printer Norml LIVE PLC Questions And Answers 2 October 14th, 2008 01:16 PM
ASCII Modbus Example code WEP LIVE PLC Questions And Answers 2 August 21st, 2002 01:25 PM


All times are GMT -5. The time now is 01:36 PM.


.