1756-L71 Connection to radio modem SRM6330

lrahman

Member
Join Date
Oct 2017
Location
Dubai
Posts
21
Please any body help me how to connect a DATALINK radio modem SRM6330 to Allen Bradley Controller 1756-L71 using Ethernet link between the two? Thanks
 
The Data-Linc SRM6330 is transparent at the Ethernet level so the only thing you need to do is connect an Ethernet cable between the two. There isn't any programming needed in the ControlLogix. The SRM6330 does require at least one master and one remote in order to operate.
 
Thank you sir, but when we use one SRM6330 as master connected to L71 Controller, we use MSG message instruction to read and write data from slave SRM6330+L71 Controller. in master PLC we define communication path as 2,1 to read/write data from slave controller via DF1 (Serial port), then if we use SRM6330 what should be the communication path in MSG instruction. Please advise
 

Similar Topics

Environment: MMI Side: Intouch 10, ABCIP.5 connects with one 1756-L71; ABTCP.1 connect with few PLC5 1785-40E PLC side : 1756-L71 5570 Controller...
Replies
6
Views
2,339
I am trying to connect directly to the 1756-L71 processor I have using a USB cable. The manual says if you have RSLINX 2.57 installed (I do) that...
Replies
2
Views
2,993
Hello, I have a pair of redundant 1756-L71 controllers rev 24. These controllers currently have produced and consumed tag interfaces to 3 other...
Replies
2
Views
160
Hi All, We have a number of old discontinued 1756-L1 PLC systems that we are trying to support but recognize that we need to start preparing to...
Replies
5
Views
968
Two days ago I used Control Flash Plus to upgrade the firmware on a 1756-L71 controller from v20.13 to V35.12. The upgrade aborted soon after it...
Replies
8
Views
1,126
Back
Top Bottom