Studio 5000: Working on Structured Text Commands, and...
AutomationTechBrian
Jul 2013
St. Cloud, MN
671
I'm working on learning Structured Text, and I'm stuck on something so simple:
I have an If-Then statement using Bool tags, and I'm having a hard time understanding why this doesn't work...
If Homing_Process and NOT Homing_Complete then Machine_State_Homing := 1;
NOT is not working. Both Homing_Complete and Machine_State_Homing are 1. Is there another way to write the not-bit?
I'm hovering the cursor over the tags, which shows me the current value. Everything starts out 0. After homing, all three tags are 1s. I could do this simply in ladder logic, but I can see ST will be a great tool, once I learn it better. So I'm working through the learning curve.
If it's the same as Siemens you have set the bit but have no reset.
You can use
else Machine_State_Homing := 0;
or (in Siemens at least) you could simply use
Homing_Process and NOT Homing_Complete;
Have you checked your syntax?
If Homing_Process and not Homing_Complete then
Machine_State_Homing :=1 ;
End_if;
This works for me.
Steve
I know nothing about structured text but do spend a too much time on PLCtalk.
maybe this
If Homing_Process and NOT Homing_Complete then Machine_State_Homing [:= 1]
See http://www.plctalk.net/qanda/showthread.php?t=78088
This is correct. If your familiar with ladder, think of :=1 as a OTL. You need a condition of := 0 to “unlatch” your expression.
Think of [:= 1] as an OTE, the bit will be a 1 if the expression is true, in other words, not retained.
The logic in the OP
is equivalent to an OTL (latch), so if ever Homing_Process was 1 and Homing_Complete was 0 on the same scan, then Machine_State_Homing would have been assigned a 1, and would remain 1 after either of the inputs changed, no?
Just got off the phone. I haven't read your responses yet because I'm on-site. I found a solution before he did. I switched it around:
Machine_State_Homing := Homing_Process and NOT(Homing_Complete);
That worked. I don't know why the other didn't, but I'll look at that later on when I'm home.
ST will be a big deal for me. The math is so much easier. This is changing the way I think about solutions.
Yah, that changes the logic from an OTL to an OTE i.e. Machine_State_Homing is assigned a value on every scan; in the OP logic that is not true.
Specifically:
This:
is equivalent to this:
Code:
   Homing_Process  Homing_Complete  Machine_State_Homing
---] [-------------]/[--------------(L)--------------------
and this:
(and probably also this:
Machine_State_Homing := Homing_Process and NOT Homing_Complete
Code:
Sorry I didn't see it sooner.
I personally like the "equation" form (A = B AND C). It is just more clear to me. However, if you are more of an IF-THEN type person, the OTE equivalent requires an ELSE:
IF (B AND C) THEN
A := 1
ELSE
A :=0
END_IF
Keith
P.S: Sorry, missed the post by bb76 which says exactly the same thing. My eye skipped right over that.
I am using Studio 5000 Version 30 and Compactlogix. I have a recipe created in a UDT structure, with a string value called name. There are 50...
5,574
Hello everyone, I'm new here, I hope someone can help me. I've been trying to install EDS files to my Studio 5000 with the EDS tool installer but...
121
Hi Everyone, I am facing an issue while installing the STUDIO 5000 in my windows 10 PC. During installation I am getting an error that " Error...
187
I am connecting to a remote device. When attempting to upload I receive an error that states: Error: Auto_Functions: The Import was aborted due...
190
