Studio 5000 Find instruction help! Not working??
lunenburger
Jul 2008
Summerside
209
I am using Studio 5000 Version 30 and Compactlogix.
I have a recipe created in a UDT structure, with a string value called name.
There are 50 Recipes in the RecipeList array
I want to take a string value called "ScannedRecipe" and have the PLC go down the list of 50 Recipes and find the name that matches, and load the recipe number into the CurrentRecipe list (see pic 1)
I am trying to use the find instruction, and there are no errors but it is also not working. (see pic 2)
I feel that i may need to use a wildcard or something instead of the zero in the search tag (RecipeList[0].Name but nothings working.
If anyone knows a better way i am open to other options.....
Thanks in advance
Got it working with the FSC instruction. (see pic)
Have to unlatch the .IN and .FD bits of the RecipeSearch control word in the next rung....
Before COP instruction, for FIND instruction you need to analyze that Result is >0 because it passes power all the time, found or not.
For FSC, you need to check for .FD bit
In the Not Found Branch I would also add a XIC FSC.DN Bit. That way you know the search has completed and Not Found.
You should try to go back to FIND instruction.
FSC is probably overkill for this simple task.
But if you want to scan through an array then FSC is the way to go
Hi, When installing new PC, how do I find what EDS file that is used for a device in an existing project. Without access to Studio 5000 on the...
5,492
Hello! I am in the process of converting a Horner program into Studio 5000 for a customers gasifier. The Oxygen sensors are +/- 1000 mV. The...
2,667
Hi Everyone. Not posted on here for a long time, but I am hoping someone can help me. I am doing a differential pressure calculation in a L27ERM...
267
Hi, how do I convert 2x Integer registers to a Real? The two integers are from Modbus registers that contain a floating point value, I need to...
121
What is the best way to extract the hour and minute from the register that comes from Yaskawa VFD. In studio 5000 I have a register saved as INT...
125
