Common ground or 0V
PL_c
Apr 2018
LT
Hi, I have two different power supplies.
First 5A DC, second 20A DC
I will use them for PLC's.
How i should connect them together.
Please look at pictures.
Thank you.
You don't have to connect together, however, if you need the same "Reference Point" for both then you should connect as shown in figure 2.
I use seperate plc’s who are power supplied from different power supplies and these plc’s share with each other inputs/outputs.
Any power supply output needs a reference to ground. It can not be floating.
If it were floating and its cables pass next to other cables with strong dv/dt like those that use PWM, voltages in the range of thousands volts can be induced respect to earth in the floating side.
For avoid this the usually way is to connect the 0V output to ground but only at one point, usually at power supply output terminal, but never use the ground circuit as power supply common. The common must be a separate wire.
Of course to achieve this the power supply must have the output isolated from input. The same applies for transformers.
I don't get the purpose of #1 as both supplies are wired to the same neutral anyway, according to the schematic.
As for connecting both output commons together, yes if they share devices. An example is analog sensors powered by G1 and their output is connected to PLC inputs that is powered by G2. In that case both PLC Analog sensors need to share the same reference point/common.
And as Ife stated grounding has to also be considered.
We switched from a SLC5/04 to a 5069-L320ER, and the SLC's NI4's were replaced with the 5069-IY4, which is a pretty neat card; however, the IY4's...
1,773
Wondering what are the pros/cons of tying Power +24VDC supply Common to chassis (earth) ground. Is it OK to do so? I have seen some control...
53
15,014
Good Afternoon , I'm sure there are many Ishida Muti-Head Weigh Systems . We have a Ishida CCW-M-214W Multi-Head system . We are...
609
Hi, I am connecting an Autonics make stepper driver type, MD5-ND14 to a Kinco PLC (K205 series) this has a sourcing output which cannot be...
1,140
I speculate that PLCs translate the language from programmers (e.g Ladder Logic, SFCs, Structured Text) into a common intermediate language...
4,277