PLC GE-Fanuc can Online Edit Program while CPU Run Time ?
Dear Everyone
I work with PLC GE-Fanuc. But I don't know that "PLC GE-Fanuc (Series 90-30 and VersaMax) can Online Edit Programming while CPU Runtime ?" I used to work with PLC Allen-Bradley and I knonw that Allen-Bradley can Online Edit Programming while CPU Run Time. But for PLC GE-Fanuc, I don't know. Please inform me about Online Edit Programming of PLC GE-Fanuc Thank You |
![]() |
![]() |
#2 |
Lifetime Supporting Member
![]() ![]() Join Date: Mar 2008
Location: Kansas City
Posts: 237
|
The GE-Fanuc PLC line was sold to Emerson a few years ago.
The 90-30 and VersaMax do not have online editing, but you can download changes to the 90-30 while it is running. The VersaMax depends on the model and version of firmware as to whether it can download while running. The newer Rx3i line has online editing. If you want to save to flash memory, you will have to stop the PLC for all types. |
![]() |
![]() |
#3 |
Member
![]() ![]() Join Date: Dec 2011
Location: Bangkok
Posts: 51
|
Thank You dYoast
Before I post this question, I unintentionally online edit program by change instruction in Ladder (from ONDTH to TMR). Then all ladders colour change to pink colour ! In my understand as your described ; 1. I can download edited program into CPU again ? 2. I must stop CPU before download ? Do I understand correct ? Last edited by alpine; June 23rd, 2022 at 02:01 PM. |
![]() |
![]() |
#4 |
Lifetime Supporting Member + Moderator
|
Question #1: Yes
Question #2: No. You only need to stop the CPU from running the program is when you make changes to hardware configuration. Program changes can be made without stopping. |
![]() |
![]() |
#5 |
Member
![]() ![]() Join Date: Dec 2011
Location: Bangkok
Posts: 51
|
Thank You Steve
|
![]() |
![]() |
#6 |
Lifetime Supporting Member
![]() ![]() Join Date: Nov 2011
Location: Corona, CA
Posts: 2,038
|
Yes, you can edit online if not making hardware configuration.
You will also need to verify how you are using the flash memory if your CPU supports it. It maybe configured to "always load from flash". Why? If you edit online, it is not saved to the flash memory. You will have to stop the CPU then download and verify you are also downloading to FLASH Memory also.
__________________
****Control Freak**** Net is where I be and Nathan is me. I have a condition called "The Knack". https://www.youtube.com/watch?v=g8vHhgh6oM0&t=2s |
![]() |
![]() |
#7 |
Member
![]() ![]() Join Date: Dec 2011
Location: Bangkok
Posts: 51
|
Thank You Netnathan
As your described If I would like to download to FLASH memory, I must stop CPU before downloading. If I would not like to download to FLASH memory, No need to stop CPU ! Do I understand correct ? And I have read about hardware of PLC GE-Fanuc ; RAM memory need to use battery to store programming data when power turn off. But FLASH memory no need to use battery. Do I understand correct ? |
![]() |
![]() |
#8 |
Lifetime Supporting Member
![]() ![]() Join Date: Nov 2011
Location: Corona, CA
Posts: 2,038
|
Yes.. on all questions.
__________________
****Control Freak**** Net is where I be and Nathan is me. I have a condition called "The Knack". https://www.youtube.com/watch?v=g8vHhgh6oM0&t=2s |
![]() |
![]() |
#9 |
Lifetime Supporting Member
![]() ![]() Join Date: Nov 2011
Location: Corona, CA
Posts: 2,038
|
Are you using Machine Edition PLC software?
__________________
****Control Freak**** Net is where I be and Nathan is me. I have a condition called "The Knack". https://www.youtube.com/watch?v=g8vHhgh6oM0&t=2s |
![]() |
![]() |
#10 |
Member
![]() ![]() Join Date: Dec 2011
Location: Bangkok
Posts: 51
|
Thank you Netnathan
I use Machine Edition Software. |
![]() |
![]() |
Bookmarks |
Currently Active Users Viewing This Thread: 1 (0 members and 1 guests) | |
Thread Tools | |
Display Modes | |
|
|
![]() |
||||
Thread | Thread Starter | Forum | Replies | Last Post |
Allen Bradley Free running counter or clock - CST - and time synchronization | V0N_hydro | LIVE PLC Questions And Answers | 7 | August 15th, 2019 12:18 PM |
GE Fanuc 90-30 PLC | Stixs | LIVE PLC Questions And Answers | 15 | January 31st, 2018 11:36 AM |
Back up GE Fanuc 90-30 PLC program | paramesium | LIVE PLC Questions And Answers | 4 | June 14th, 2015 10:49 PM |
WinCC 7.0 PLC Time Sync | erdemsvri | LIVE PLC Questions And Answers | 0 | February 22nd, 2011 08:00 AM |
Series one GE Fanuc plc | sandro.chiarle | LIVE PLC Questions And Answers | 7 | September 15th, 2002 06:25 PM |