Old March 11th, 2004, 03:46 PM   #1
Anibal Hernandez
Member
Puerto Rico

Anibal Hernandez is offline
 
Join Date: Aug 2003
Posts: 71
What is the best way to send 4 signals to a counter?

What is the best way to send 4 signals to a counter?

On a Micrologix 1000 I need to show 4 counts on every cycle of the press. That is every time the press comes down and up the counter must be counting by fours.

Assuming Machine is turned ON for the first time and the counter is reset to zero, first machine cycle the counter is 4, the next machine cycle the counter is 8, then another cycle completes and the counter is 12…. So on and so forth.

What is the best way to send 4 signals to this counter? This is a regular counter that increments every time a pulse is received.

Andy
  Reply With Quote
Old March 11th, 2004, 03:55 PM   #2
Allen Nelson
Member
United States

Allen Nelson is offline
 
Join Date: Apr 2002
Location: West Chester, PA
Posts: 1,368
For ideas...

See THIS THREAD
__________________
©¿©¬
  Reply With Quote
Old March 11th, 2004, 05:26 PM   #3
chavak
Member
Malaysia

chavak is offline
 
chavak's Avatar
 
Join Date: Jul 2002
Posts: 620
Another counter method -
Attached Images
File Type: jpg press.jpg (19.9 KB, 224 views)
  Reply With Quote
Old March 11th, 2004, 07:20 PM   #4
Anibal Hernandez
Member
Puerto Rico

Anibal Hernandez is offline
 
Join Date: Aug 2003
Posts: 71
Allen Nelson:

Thanks for the link, it really helped a lot.


chavak:

The application call for a real hardwired counter. Your suggestion will work great for an internal one.

Thanks guys

Andy
  Reply With Quote
Old March 11th, 2004, 11:16 PM   #5
Lancie1
Lifetime Supporting Member
United States

Lancie1 is offline
 
Lancie1's Avatar
 
Join Date: Jul 2003
Location: Alabama
Posts: 9,999
Andy,

I think you are talking about a physical counter, instead of a PLC "software" counter like most of use here on a PLC site would assume.

To change one count into 4, you would have to have a circuit board that takes 1 pulse and converts it to 4 pulses (a pulse generator, pulse extender, or pulse stretcher). There are such solid state devices, and I am sure someone here knows how to build one from scratch. I used to know that, but have forgotten much of electronics design.

You can of course take a low-end PLC and put 1 pulse in and get a rapid 4-pulse output, using some software timers and relays. Thay may after all be your easiest solution IF you have to keep the existing counter on the existing machine. If you can change out the counter, you can probably find a BCD (Binary Coded Decimal) counter that can be wired to count by 4 instead of 1.

Last edited by Lancie1; March 11th, 2004 at 11:19 PM.
  Reply With Quote
Old March 12th, 2004, 04:33 AM   #6
Anibal Hernandez
Member
Puerto Rico

Anibal Hernandez is offline
 
Join Date: Aug 2003
Posts: 71
Thanks everyone for the answers.

I resolved the issue with 3 TON and a One Shot instruction. This Forum has to be the best there is, very knowledgeable members who are eager to help.

Andy
  Reply With Quote
Old March 14th, 2004, 05:27 PM   #7
chavak
Member
Malaysia

chavak is offline
 
chavak's Avatar
 
Join Date: Jul 2002
Posts: 620
Andy,

You got your logic to work, that is important.
But, you mentioned 3 timers and a one shot. So thought of posting another method. Just for your reference.
Attached Images
File Type: jpg press.jpg (55.9 KB, 137 views)
  Reply With Quote
Old March 14th, 2004, 05:43 PM   #8
Anibal Hernandez
Member
Puerto Rico

Anibal Hernandez is offline
 
Join Date: Aug 2003
Posts: 71
chavak:


I love your solution, like it so much that I will use it in my logic.
Sometime I'm just amazed at the many ways you can achieve basically the same result with so few rungs.


Thanks
  Reply With Quote
Old March 14th, 2004, 06:06 PM   #9
Anibal Hernandez
Member
Puerto Rico

Anibal Hernandez is offline
 
Join Date: Aug 2003
Posts: 71
chavak:


I noticed you are using a Constant value in the LIM instruction. Wouldn’t' you get an error.

Don't you have to compare to a Word instead of a Constant?

Andy
  Reply With Quote
Old March 14th, 2004, 08:10 PM   #10
Doug-P
Member
United States

Doug-P is offline
 
Doug-P's Avatar
 
Join Date: Jun 2003
Location: Pa
Posts: 1,244
Quote:
Originally posted by Anibal Hernandez
chavak:


I noticed you are using a Constant value in the LIM instruction. Wouldn’t' you get an error.

Don't you have to compare to a Word instead of a Constant?

Andy
No. Constants or memory locations are acceptable arguments for LIM instructions. You can also use indirection and I'm pretty sure indexed addressing is also legal.
  Reply With Quote
Old March 15th, 2004, 12:01 PM   #11
panic mode
Member
Canada

panic mode is offline
 
panic mode's Avatar
 
Join Date: May 2003
Location: Toronto, Canada
Posts: 1,962
All of this might work for press application but depending
on specific needs it might not be best solution.
Why count by 4? Because press makes four parts with each stroke?

A while ago I was doing something similar where machine
had two stations. Both were running same process but
running completelly independant from each other.

Customer wanted ONE external counter to count all parts
produced. The problem was that we wanted perfect result
while stations were not synchronized in any way.
In other words "Part_Complete" signals could happen at
any time (even at the same time or with very little delay).

Solution was to use one shot from each "Part_Complete" to
increment internal counter but only if the other one shot
was off. If both were on, increment by two.

Then there was a rung that was generating pulses for the
external counter. This would run while the internal counter
was not equal to zero. Every outgoing pulse would also
reduce accumulated value by one.

Just a tought...
  Reply With Quote
Old March 15th, 2004, 12:09 PM   #12
Anibal Hernandez
Member
Puerto Rico

Anibal Hernandez is offline
 
Join Date: Aug 2003
Posts: 71
panic mode:


I appreciate your thoughts. This is only one station small press machine with 4 knives lowering along with the Ram and cutting flashes-spruces out a plastic molding part. The way chavak suggested it would work just fine.

Thanks

Andy
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
Need help with counter in Siemens S7-300 lostpatrol LIVE PLC Questions And Answers 6 April 12th, 2011 04:59 AM
Filtering Signals in Ladder Code - HELP! foamman LIVE PLC Questions And Answers 8 February 1st, 2005 07:02 PM