Because data space is so precious in the old RIO architecture, the PanelView 1200 and 1400e (and maybe even the PV Standard) allowed you to define an HMI tag that used only a certain number of bits out of a data word.
Binary-Coded Decimal was one way that old controllers (especially the PLC-2) encoded analog data. You'll find that some 1771 family I/O modules allowed you to set up the data to be BCD format.
If you're migrating the PanelView 1400e to a new platform, it's best to change the network as well. If you can't change the network and loosen up the data packing, then you'll have to go through some careful expression math to mask and shift the data for those tags.