I once heard there was a rule for running conduit containing 480V into the side of a machine at a horizontal angle. If it comes straight down from the ceiling to the machine, it could cause a arc from condensation build up.

Is there any truth to this?

If so, do you know where in the rules it is?



Thanks in advance!
 
If there is enough moisture in your atmosphere for you to experience condensation build up in your conduit, then said conduit is not fit for purpose and your mains cables should be IP rated for the job. Enclosed cable and glands from source to cabinet.
 
You will get condensation if there is a temperature difference between the ends of the conduit. E.g. if you're running the conduit from a roofspace into an air conditioned food processing hall, then you WILL get condensation. This applies whether the conduit is vertical, horizontal, or put in by crazy-eye johnston on a 27 degree angle.

This doesn't just apply to your mains, either. Obviously the SAFETY risk is higher with higher voltage, but the functionality/equipment risk is the same with any type of cable.

In this situation I always specify the board to be bottom entry, run the conduit down level with the bottom of the panel and then loop the cables into the bottom of the board through a gland. Then stand back and watch all the condensation dripping harmlessly out the bottom of the open conduits, and be thankful it's not dripping into your main isolator or your PLC ;)
 
Ditto to ASFs comments. You can also use silicon (silastic) food rated and seal BOTH ends of the conduit. To prevent air flow from both temperatures.
I prefer ASF method though.
 

Similar Topics

I have no experience with Eaton HMIs. I downloaded the Galileo software and I am trying to get the file on a HMI (XV-102-H3-70twrl-10) to modify a...
Replies
5
Views
127
How to fix if appears code “$115 plc-restart running” on the screen OP17
Replies
5
Views
248
Here's what happened, Operator turned on the disconnect for an auger while it was still running to cut power. Auger DID in fact turn off, but the...
Replies
8
Views
337
Hi! I am trying to run the 'SimpleSample' (https://infosys.beckhoff.com/content/1033/TF5100_TC3_NC_I/Resources/3438746891/.zip ) to understand the...
Replies
2
Views
106
A new point I/O rack is to be hooked up with the running PLC. In point I/O, it is supposed to be the OA4 card to be installed as per the...
Replies
1
Views
92
Back
Top Bottom