Siemens Micromaster 440 Locked Parameters

douglasfcx

Member
Join Date
Mar 2014
Location
Gyn
Posts
2
I have a Siemens Micromaster 440 (6SE6440-2UC25-5CA1) with encoder module (6SE6400-0EN00-0AA0) and Profibus module (6SE6400-1PB00-0AA0).
I'm unable do access multiple parameters via BOP, even parameters with access level 1, like P0004. I'm unable to access parameter P0970 too. So I'm unable to reset the driver to factory settings. The driver is in profibus network. I tryed to disable the driver and change P0003 to 3 and 4, but the parameters still locked.

There is a way to unlocked the parameters of Micromaster 440 by BOP?
 
It may be P0927

Hi,

It may be caused by parameter P0927. To be able to change parameters using all communication channels it sould have as value "b--nn".

Best regards,
Ricardo Paz
 

Similar Topics

My tutor asked me for this small project: using S7-200 control MM440 with PROFIBUS. Because S7-200 with PROFIBUS module EM277 can only be PROFIBUS...
Replies
4
Views
2,973
fault A0501 (i.e current limit ) displaying whwn i replace siemens 420 drive with mm440. all parameters are crosschecked. please help to...
Replies
4
Views
1,550
I am trying, for the first time, to write values to the control word of a Micromaster 440 using an S7-300 PLC. I barely know what I'm doing, and...
Replies
4
Views
2,572
Hello good day : micromaster have a 440 installed on a machine, when I push button start machine micromaster machine works well, up to speed and...
Replies
3
Views
2,169
Hi All, Today we had a drive die on us. There was no backup but we have a duplicate drive in service. Can't upload via AOP or starter but Siemens...
Replies
11
Views
11,426
Back
Top Bottom