Problems with SLC 5/05 MSG instruction over Ethernet communication
alex08
Sep 2008
SLP
Hi, I have a problem with a cpu slc 5/05 (1747-L552), 32k Mem 0S501 series C, I am using the MSG instruction to ethernet communication, it works for a few days very well, but later the communication turns to slow, and sometimes stop for complete. The way that the communication is restablished its making a cycle power to the processor. Below appear a part of the logic that I am using to send and receive information to DVT system by ethernet. Somebody knows if there is another way to configure this instruction and never gets faulted?
I dont think so, agree to the posts that I been reading the problem is about the buffer that this instruction use, it gets full or something wrong happens, attached I send part of the logic.
Here is the configuration that I am using in the MSG instruction (read/write), I am using 2 instructions to read and 1 to write, the logic is the same in the 3 instructions (shown in my last post).
Ok, these screen captures are getting old real quick...I think you can actually post images so we won't have to unzip everyone.
You posted the message configuration, I asked about how you were managing the execution of your messages.
The execution is direct to the plc scan,I mean I am sending and receiving data all the time, you can see these in the logic shown in this post.
most likely your buffers are slowly filling up until they can't do any more messaging.
Try conditionalizing your messaging. How often do you really need the data?
So your bits such as N24:0/15 are not managing the execution of the MSGs at all?
You should at least inhibit the rung as long as the message is enabled...XIO MG.en...to keep it from firing continuous. It does no good besides filling up the buffers.
Not sure this is your problem, but it will probably cause problems with the buffers.
How many Ethernet messages are you executing? 4?
you are hammering the comm port hard until a buffer queue full error occurs that can only be solved by cycling the power to the plc.
manage the comms as an example such as this way. Only during a certain time slice will a message be triggered
Thank you guys...
I'll test some changes in the logic and I'll post any advance of this topic...
Regards!
Hi, I try to solve the problem restricting the messages when I dont need the results from DVT system, and also I include a timer in the logic to trigger each message only during a certain time slice, and I still having the same problem. Here is part of the last version of the program. Any other idea to solve this?
try the message isntruction without the unlatch after each MSG. Unlatching the bit will cause the MSG to execute as many times as possible during the 200ms each MSG is true. This is eventually causing a buffer overflow that can only be reset with a power off.
Also test the etherent cable between processors with an ethernet tester
Hi, ive been having problems with existing messaging system on a dh-485 network with 4 SLC5/03 plc's. The system has been in place running...
9,227
Hello. PLC beginner here, so apologies in advance for any incorrect terminology or poor communication. I have an SLC 500 Thermocouple/mV Analog...
663
Hey everyone, I am trying to communicate with a Slc 5/04 plc using the 1747-cp3 cable, RS232-DF1 driver and a laptop. I tried using a serial to...
3,167
Hi all, I have an slc 5/05 and am trying to read data from an 193-etn using the eem instruction as described in the instruction, but I cannot get...
1,812
Hello, I have a problem and certainly just one of many to come as I become more involved with PLCs We've got a panelview 1000 connected to a SLC...
3,196