ERROR TRANSLATION MOV PLC 5 to STUDIO 500

VickyPumero

Member
Join Date
Aug 2015
Location
Miranda
Posts
6
Good morning.

I am making a migration of a control logic from RsLogix5 to Studio 5000. One of the errors I have



The two points that appear in the tag of the source that instruction or operation means?


Thanks for the help you can give me (y)

15.PNG
 
The basic problem is that RSLogix5000 cant use a pointer from an array. It has to be a stand alone tag. But the next problem you will have is 5000 does not allow indirect pointer to arrays. But fear not there is a way. See my thread here on how to use a message instruction for the PLC to read to itself and then you can indirect tags and tag arrays.
http://www.plctalk.net/qanda/showthread.php?t=105602
 