Motor with no load
Karsten
Feb 2006
Odense
158
Hello,
If I have a 5.5 kW electrical 3 phase motor with no load(free axis) and measure the active effect, what value in kW can I expect roughly?
Hello,
The active power will be close to 0 kW.
Law of Conservation of Energy : if the motor does not do any work it will not consume energy from the electrical supply, it will only consume the small losses due to friction and heat
All the current you can measure in the cables is reactive intensity and the power factor will be very close to 0
When I test a motor (full voltage) with no load and its current is higher than 25% of full load , my decision is not to buy it.
In my experience, something in the neighborhood of 30% of FLC is typical for an unloaded motor. Then again, as jraef said, it varies with motor design.
Low speed motors tend to draw more no-load current. Motors designed to provide high starting torque will also draw higher no-load current.
The motor that generates more reactive power at no load usually has bigger and more robust windings, which is not a bad thing.
And if the plant has its reactive compensation system there should be no problem.
Siemens used to have a motor plant here in Colombia , they closed it years ago.
All motors from that plant used to consumed almost 50% of full load current with no load. No body wanted to buy those motors.
That current does not count in the energy consumption.
Connect three capacitors in parallel with the motor and you will see that this current is greatly reduced.
If you are talking about a motor with permanent magnets on the rotor, like a typical servo motor, the current/power draw will be very low with no load. If it's an AC induction motor the magnetizing current can be a considerable value depending on the design/purpose, but most drives typically factor this in and report low power usage despite the higher magnetizing current.
Heh!
Love your signature line.
Well, almost. While the the total kVA value of the magnetizing voltage and current is not converted to work (it is returned to the line or drive on the next half cycle) that current still needs to run through the motor supply conductors and the motor windings, where some of it is converted to heat. So, all other things being equal, a motor that draws lower no-load current will be more efficient, at least at partial load.
Keith
The losses through the cables will be comparatively as small as those of the machines that are consuming active energy.
And I don't think that in most industrial plants they worry about cable losses.
My R55 Ingersollrand is tripping on motor overload and im falling to see the trip history it is writing Acquarring texts
132
Any panel I've built with contactors and overloads has been 3 phase. I'm now quoting on one with some small single-phase loads. Definition of...
24
5,649
Simple question that I keep forgetting the answer to: When a VFD is running it's motor auto-characterization routine (static and rotating) where...
1,933
It is said motors are can be overloaded for a duration of time but I can not find a document or formula which clearly states how long I can...
3,151
I have a problem with a DC Motor of 250Kw. We try to process hot steel bars. We are using these motors with speed control in a roughing chain of...
3,152
