Guys, it is a current LOOP. As long as the current travels in the same direction through each device, electrically the order does not matter.
In real electron flow (not conventional flow), current flows out of the power supply on the negative terminal, enters most negative side of the next device, leaves + terminal, goes to most negaive side of second device, leaves plus terminal, goes to most negative side of third device, leaves plus terminal, and finally arrives back at the power supply + terminal.
It is possible that the added reistance of the extra plc input is changing the loop current some, but probably this is not a significant error source. To make the operator display readings of the two PLCs match, you must adjust the scaling factors in each PLC program, and maybe also in each operator panel display. Most likely they are not scaled with the same instructions, or use different scale factors.