Working with Guardmaster 450L-B. Is there a distance too close for these modules to be mounted? These are about 20" apart. Can't get the safety outputs to come on and have checked everything thoroughly.
 
Yes there is a minimum distance. The distance is based in what the resolution of the light curtain is.
In the manual it calls out the distances. I think 24" is minimum. Dont hold be to that number. It has been several years since we had that problem.
 
450L-B:
Resolution 14 mm (0.56 in.): 0.5…4 m (1.64…13.12 ft)
Resolution 30 mm (1.19 in.): 0.9…7.0 m (2.95…22.97 ft)
Reduced operating range (selected with DIP switch):
Resolution 14 mm (0.56 in.): 0.9…2 m (2.95…6.56 ft)
Resolution 30 mm (1.19 in.): 1.2…3.5 m (3.94…11.48 ft)

So looks like 20" would be the min if using the 14mm version in normal range.
 

Similar Topics

Hello all. I am purchasing a CompactLogix to use as a server which will host 4 other PLC's (2 ControLogix, 2 Beckhoff) and a Fanuc RC. The current...
Replies
5
Views
918
Hi All, On our site, we normally use trapped keys for our safety gates, however, for our newest project, I have been told that we will be using...
Replies
1
Views
1,012
I am working on a project where an AB Guardmaster 440C is the logic solver for some SIL-rated interlocks. I need to be able to send reset bits...
Replies
0
Views
742
Wizards, A little something out of the norm, I have a LoTo station that someone built for training purposes. It never got completed and the box...
Replies
2
Views
1,981
Good Evening , I have some Rockwell Light Curtains and Guardmaster 440C-CR30 Configurable Safety Relays . I was wondering if there is any...
Replies
2
Views
1,389
Back
Top Bottom