PLC/HMI that can have a program using RTC
Hello everyone and thank you for your assistance before hand.
I have a request from a customer that wants to run a conveyor for only 15 to 30 seconds twice a day. No big deal easy enough. The problem is that this customer wants the conveyor to run only at 5 AM for 15 to 30 seconds and then be off until it is turned on again at 7 PM for 15 to 30 seconds. This is an every day routine. Any help would be greatly appreciated. |
![]() |
![]() |
#2 |
Lifetime Supporting Member
|
As a starting point, what controller and other hardware does the customer have right now? What's the budget?
|
![]() |
![]() |
#3 |
Member
![]() ![]() Join Date: Sep 2019
Location: Ft Worth, TX
Posts: 7
|
Only hardware for sure is a Minarik DC drive. Budget is a low as possible. I have been looking at a Maple HMI/PLC unit to see if it could provide this function but have not found that information yet.
|
![]() |
![]() |
#4 |
Lifetime Supporting Member
|
Click PLC with Ethernet has a RTC. If you need an HMI to go with it, my preference is Red Lion but for cheaper there are C-Mores that work well with a Click.
https://www.automationdirect.com/adc...its/c0-10dre-d That one has Ethernet and relay outputs. You can save a few dollars by going with the Standard instead of Ethernet version and if you want an interposing relay, you can get one with transistor outputs in either family. In my opinion, always go with the Ethernet models.
__________________
You can choose a ready guide in some celestial voice. If you choose not to decide you still have made a choice. |
![]() |
![]() |
#5 |
Lifetime Supporting Member
|
Why not use something simple like a Siemens Logo or similar? They are inexpensive and simple.
|
![]() |
![]() |
#6 |
Member
![]() ![]() Join Date: Sep 2019
Location: Ft Worth, TX
Posts: 7
|
Liam
My company mainly uses Rockwell for PLCS and HMI. We have used Maple systems before as well though. |
![]() |
![]() |
#7 |
Lifetime Supporting Member
|
Rockwell have a similar product to the Logo called Micro 800. I have never used one, but I am sure it would have similar functionality.
|
![]() |
![]() |
#8 |
Member
![]() ![]() Join Date: Sep 2019
Location: Ft Worth, TX
Posts: 7
|
Thank you Liam. I am looking into the Rockwell as well as the Maple systems. Just trying to see which one is cost effective and will still allow me to use the RTC as part of the ladder logic for the program.
|
![]() |
![]() |
#9 |
Lifetime Supporting Member
![]() ![]() Join Date: Nov 2006
Location: UK
Posts: 6,143
|
Central heating controller/one of these?
__________________
S7-300 to 1500 conversions done - email to s7conversions@hotmail.com Last edited by L D[AR2,P#0.0]; January 13th, 2021 at 01:08 PM. Reason: additon |
![]() |
![]() |
#10 |
Member
![]() ![]() Join Date: Sep 2014
Location: NC
Posts: 836
|
If it's Rockwell, a MicroLogix 1100/1400 would work as well if you're more familiar with those.
|
![]() |
![]() |
#11 |
Lifetime Supporting Member
|
To what accuracy is the turn-on event 5am and 7pm expected? 10minutes? 100ms? Is drift acceptable i.e. 05:00:00 one day and 05:00:01 a week later?
What determines how long the conveyor runs? is it the same every day? does someone turn it off manually? Should the conveyor run on weekends? What is the environment (indoors? outdoors? panel enclosure)? We have battery-powered "candles," probably from Walmar, that we put in the windows every year around 01.December. when you screw in the bulb at 4pm, they light stay lit for 5-6h; with no more intervention they repeat that every day at the same time until we unscrew the bulb. Even a minimal PLC is more than this project requires; but the greater bulk of the cost is going to be labor for the wiring and programming. So anything that has a clock could potentially work; this could be done in a spare laptop with a printer port and GWBasic. |
![]() |
![]() |
#12 |
Member
![]() ![]() Join Date: Jan 2006
Location: Finland
Posts: 1,528
|
Timer relay as LD writed would be most cost effective.
It only needs AC-supply and wiring from relay out to VFD start input. |
![]() |
![]() |
#13 |
Member
![]() ![]() Join Date: Sep 2019
Location: Ft Worth, TX
Posts: 7
|
Thank you all for the valuable inputs. I have narrowed down my choices and will submit it to my customer for their approval.
|
![]() |
![]() |
#14 |
Lifetime Supporting Member
|
Sounds like a poop collection system at a Diary Farm.
Clear the contents after each milking cycle. Almost any smart relay should work. I use these for home projects. https://www.factorymation.com/SG2_PL...feature_PLR_SB
__________________
Certified Siemens Functional Safety Professional, ID: SFSP17010238 https://azr.com/ Last edited by Ken Moore; January 13th, 2021 at 04:26 PM. |
![]() |
![]() |
Bookmarks |
Currently Active Users Viewing This Thread: 1 (0 members and 1 guests) | |
Thread Tools | |
Display Modes | |
|
|
![]() |
||||
Thread | Thread Starter | Forum | Replies | Last Post |
Studio 5000 Program Parameter Connections | theColonel26 | LIVE PLC Questions And Answers | 7 | October 25th, 2019 09:55 AM |
How to switch drivers | lbeh | LIVE PLC Questions And Answers | 7 | December 11th, 2014 03:11 PM |