How to set EtherCAT slave address on B&R PLC
SirCumference
Aug 2014
Milwaukee
24
Hi, I've got a B&R X20CP3584 PLC with an X20IF10G3-1 EtherCAT slave card. I'm trying to connect it to an EtherCAT master device (a KUKA KRC4), but there doesn't seem to be any place for me to set the slave address in Automation Studio. Does anyone know how to do this? Thanks!
Not claiming to be an expert on EtherCAT, but I thought that in majority of cases the slave address is set automatically, when the master scans the network.
The user "Ladderlogic" is right:
Ethercat Master are able to set the station address during startup.
This has to be made by the master.
This sequence is due to the Ethernet Slave hast an "IN" (IF1) and "OUT" (IF2) connection.
On Basis of the physical order the slave is recognized and identified.
Hi, I´ve got B&R PLC X20CP1382 and etherCAT modul X20IF10G3-1 and I need to communicate with Kuka KRC4 via EtherCAT. Is there some procedure how to set up communication in Automation studio 4.3.?
Thank you.
Hello, I still do not have equipment in to test. But the RTAC ladder does not have a timer reset coil. I wonder if a reset coil on Timer.IN is...
122
Hi, i am using DVP-14SS2 PLC, after program written to plc, when power is reset, plc doesn't run. always need to connect to pc for the run mode.
60
Hi need help why this “failure 5 emergency stop “ appears at every startup in the morning ? Have to shut off main switch at least 10 times on...
19
394
Omron AD081-V1 Analog Input Card Offset & Gain Adjustment Entering Adjustment Mode 1. Set the input card in adjustment mode (Turn ON Dip SW No-1)...
115
I was loading a program onto an XE1e2 PLC and it got stuck on these two windows and won't progress. It won't let me connect from the PC to reload...
99