PlantPAx Object for Controlling 2 state device

Hi,

Anyone familiar with the PlantPAx library?

I have a few simple devices I need to control. 2 outputs for open/close and 2 inputs for status opened/closed.

I could use a P_Valve or P_Pump object and rename it but curious if sometime already exists for a simple 2 state device.

Thanks in advance
  Reply With Quote
Old January 13th, 2021, 11:27 AM   #2
Ken Moore
Lifetime Supporting Member
United States

Ken Moore is offline
 
Ken Moore's Avatar
 
Join Date: May 2004
Location: North, West, South Carolina
Posts: 2,994
P_Valve sounds perfect, why change?
__________________
Certified Siemens Functional Safety Professional,
ID: SFSP17010238
https://azr.com/
  Reply With Quote
Old January 13th, 2021, 01:41 PM   #3
MorphuisOGrady
Member
Sweden

MorphuisOGrady is offline
 
Join Date: Jul 2007
Location: Kiruna
Posts: 591
Simply because it's an electrically actuated clamp and not a solenoid valve.

Sure it will fit the purpose but I was just curious if there was such an object in the library for a generic 2 state device.
  Reply With Quote
Old January 13th, 2021, 02:21 PM   #4
JeremyM
Lifetime Supporting Member
United States

JeremyM is offline
 
Join Date: May 2014
Location: Texas
Posts: 495
You could create a UDT containing a pair of DIn, DOut, and perhaps some custom commands/states that are associated among them. Think of it as an equipment module containing its control modules.

However, I lean to Ken’s idea because you could easily enough copy and rename, or rename outright, the P_Valve AOI to be “P_Solenoid”.

Last edited by JeremyM; January 13th, 2021 at 02:23 PM.
  Reply With Quote
Old January 14th, 2021, 02:55 AM   #5
cardosocea
Member
United Kingdom

cardosocea is offline
 
Join Date: Nov 2016
Location: Fields of corn
Posts: 1,776
Isn't there an AOI for this? I know there's one for n-State device, but it's likely overkill?
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
Measuring speed moving object with device connected to PC HenryLamboo LIVE PLC Questions And Answers 6 January 4th, 2006 09:18 AM
Setting up CP 343-1 card (siemens) Johnny T LIVE PLC Questions And Answers 35 August 19th, 2005 07:58 AM
Analogue Inputs - Sink, Source, Help! Yabadabadoo LIVE PLC Questions And Answers 14 January 26th, 2005 01:48 PM
Turning Device and Embossing Device ferdiecobilla LIVE PLC Questions And Answers 2 December 10th, 2003 03:01 AM
Normally open or closed or... Phil Melore LIVE PLC Questions And Answers 15 February 3rd, 2003 08:14 PM


All times are GMT -5. The time now is 03:35 PM.


.