Locale message display problem RSView Studio

Hello,

I use RSView Studio ME and RSLogix5 to program a panelview 700 plus panel.
I will using 16-bits of a word N7:0 to control a Locale message display.
When example bit 0 (N7:0/0) is high message 1 will appear, bit 2 (N7:0/2) is high message 4 appear.
The problem is when both bits are high a message 5 will appear.
I want that first the lowest message bit appear (in this case bit 0) and when this bit is low the next bit whoīs high (in this case bit 2) appear in the locale message display.
Who can help me?

Greetings,

mulderm
__________________
Netherlands
  Reply With Quote
Old November 7th, 2006, 02:14 PM   #2
SNK
Member
Canada

SNK is offline
 
SNK's Avatar
 
Join Date: May 2004
Location: Toronto, Ontario
Posts: 885
You need to write code in your PLC to use your address value.
You should also use FBC to compare a table against your faults, and use a timer to scroll the constant alarms as they arrive.
You need to write some simple logic like,
IF ALARM is true, then SET N10:0/1
If N10:0/1 is TRUE, MOVE a 1 into ADDRESS N7:0 (Your PV+ Word)
You have a lot of code to write to accomplish what you want.
Hope this was semi-helpful.
  Reply With Quote
Old November 7th, 2006, 03:08 PM   #3
mulderm
Member
Netherlands

mulderm is offline
 
Join Date: Jun 2003
Location: Netherlands
Posts: 292
Yes, I know that I must write a lot of rungs.
Is there a better way?

mulderm
__________________
Netherlands
  Reply With Quote
Old November 8th, 2006, 02:05 AM   #4
mulderm
Member
Netherlands

mulderm is offline
 
Join Date: Jun 2003
Location: Netherlands
Posts: 292
And what is the function of FBC?
Do you have an example?

mulderm
__________________
Netherlands
  Reply With Quote
Old November 8th, 2006, 05:27 AM   #5
Alan Case
Lifetime Supporting Member
Australia

Alan Case is offline
 
Alan Case's Avatar
 
Join Date: Apr 2002
Location: Wagga Wagga
Posts: 1,268
In the PV setup use the LSB option for the message.
Regards Alan Case
  Reply With Quote
Old November 8th, 2006, 03:09 PM   #6
Paul T
Member
United States

Paul T is offline
 
Paul T's Avatar
 
Join Date: Oct 2006
Location: NH
Posts: 254
Quote:
You should also use FBC to compare a table against your faults, and use a timer to scroll the constant alarms as they arrive.
If the display is for alarms, then the PV+ Alarm function will handle this easily just by linking the PLC register to the HMI. Typically, if Bit 0 and Bit 2 are both high, both alarm messages will be displayed. There is an LSB function for Alarm Setup so that only the Bit 0 message could be displayed as mulderm asked about. If these are not alarm messages, then the Multistate Indicator and List Indicator objects both work with LSB to display only the highest priority message, like Alan said.

Having said that... I gave up on the LSB because I found it harder to change messages in a list and in the PLC as programming continued. I found it a lot more convenient to just write a number and then use that in a list indicator or multistate indicator. If the PLC5 is already programmed and all you're doing is updating the HMI, then LSB is fine. If you're writing the PLC program too, then you might want to consider how much you may need to change things during debug or startup before setting the displays up as LSB.

But hey, what do I know... Frisians, eh!

Paul Tolsma <g>
  Reply With Quote
Old November 9th, 2006, 10:07 AM   #7
mulderm
Member
Netherlands

mulderm is offline
 
Join Date: Jun 2003
Location: Netherlands
Posts: 292
Paul T,

I want to use a locale message display for the 16-bits (N7:0)
and now I have some more bits (N7:1).
I can use for each message a rung with a move instruction and
for a sequence order.
Example rung 1: when bit n7:0/15 is high then move 16 to N7:10
(message 16 in the Panelview).
rung 2: when bit N7:0/14 is high then move 15 to N7:10
and further....
So I get the lowest message number on the screen.
Problem: a lot of rungs I get in the program.
Is there a better way to program?

mulderm
__________________
Netherlands
  Reply With Quote
Old November 9th, 2006, 11:20 AM   #8
burnerman
Member
England

burnerman is offline
 
Join Date: Nov 2005
Location: Huddersfield
Posts: 212
You could write a small looping routine using JMP and LBL.

Rightshift(BSR) the bits in the word array you are testing, one at a time until the LSB = 1, each time it is not = 1 leftshift(BSL) a bit in a new word array (which initially has the LSB = 1, all other bits = 0) when the LSB in the tested word array =1 stop the routine and the new word array will have a unique 1 at the same position as the lowest on bit in the tested word.

Make sure you only run the routine if the tested word array is not = 0 otherwise the program will stick in the loop forever.
  Reply With Quote
Old November 9th, 2006, 01:39 PM   #9
mulderm
Member
Netherlands

mulderm is offline
 
Join Date: Jun 2003
Location: Netherlands
Posts: 292
Burnerman,
Itīs sounds good.
Can you send this peace of program making in RSLogix5?
So Itīs better to understand.

mulderm
__________________
Netherlands
  Reply With Quote
Old November 9th, 2006, 01:52 PM   #10
burnerman
Member
England

burnerman is offline
 
Join Date: Nov 2005
Location: Huddersfield
Posts: 212
Sorry, I don't have RSLogix on this PC. Have a go yourself and post a pdf of your logic. I and others here, I'm sure, will try and help you with it.
  Reply With Quote
Old November 9th, 2006, 02:16 PM   #11
Paul T
Member
United States

Paul T is offline
 
Paul T's Avatar
 
Join Date: Oct 2006
Location: NH
Posts: 254
mulderm, the way that you're doing it is very common, and I've done that for years. You get used to it I guess!

Check the PanelView+ List Indicator object and Multistate Indicator object Help files for "LSB." This will display the desired message directly, based on the bit state and nothing else. So, you don't have to program any rungs in the PLC for it.
  Reply With Quote
Old November 9th, 2006, 02:45 PM   #12
mvandyke
Member
United States

mvandyke is offline
 
mvandyke's Avatar
 
Join Date: Jun 2006
Location: Florida
Posts: 34
Use the Multi-state indicator with a LSB trigger.



No extra PLC code is required.
  Reply With Quote
Old November 9th, 2006, 04:02 PM   #13
mulderm
Member
Netherlands

mulderm is offline
 
Join Date: Jun 2003
Location: Netherlands
Posts: 292
I will try for this tomorrow, so I let you know.

mulderm
__________________
Netherlands
  Reply With Quote
Old November 10th, 2006, 02:59 PM   #14
mulderm
Member
Netherlands

mulderm is offline
 
Join Date: Jun 2003
Location: Netherlands
Posts: 292
Wow,you are right.
I use the multi-state indicator with LSB-triggering and no
program-code is used.
Excellent!
Thanks for the help.

mulderm
__________________
Netherlands
  Reply With Quote
Old November 10th, 2006, 07:40 PM   #15
Alan Case
Lifetime Supporting Member
Australia

Alan Case is offline
 
Alan Case's Avatar
 
Join Date: Apr 2002
Location: Wagga Wagga
Posts: 1,268
Hmmm, I thought I said that in post 5.
Regards Alan Case
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
RSView Studio => Siemens via ethernet pwd666 LIVE PLC Questions And Answers 9 February 9th, 2011 08:12 AM
Test RSView Studio application on a RIO network mulderm LIVE PLC Questions And Answers 3 September 19th, 2006 04:41 PM
RSView Studio Help anks LIVE PLC Questions And Answers 4 June 21st, 2006 11:26 AM
Panelbuilder 32 to RSView Studio russrmartin LIVE PLC Questions And Answers 1 June 9th, 2006 01:39 PM
ENI - Inview message display configuration Daggi LIVE PLC Questions And Answers 0 April 21st, 2003 11:59 AM


All times are GMT -4. The time now is 05:16 AM.


.