AB HMI Comm Errors
usmcmcc
Aug 2007
Rhode Island
25
I'm using two AB Panelview 1000's with different IP addresses in separate rooms. These error messages come up randomly and numerous times daily. I have to power down and reboot. Has anyone seen this? and can you help me with this problem?
That message shows up in the RA Knowledgebase in Article ID #466346, but in that case it appears at the startup of FactoryTalk View Studio on the development PC and is remedied by replacing the corrupted RSLinxNG XML configuration schema file.
I suppose I'll ask all the questions that Tech Support would: Are the PanelViews new or have they been running for a while ? Has the problem existed since installation or has it recently started ?
Are these older PV+ version 5.10 or older terminals, or PV+6 hardware ? What exact firmware revision are you running ?
Can you tell us anything useful about the network and the controllers these terminals are communicating with ?
The HMI's are Panelview 6-1000
6.10.00 CPR9 SR4
PLC is CompactLogix 5333ER
REV 20.12
1769-L33ER
RSLogix 5000
V20.01.00
CPR9 SR5
We are an OEM and these units are about six months old and are just now being debugged on site. They have done this since the beginning. I have tried to disconnect one at a time but the issues still occurs. there are times where it goes days with no errors.
Wow, I had to really stress my memory for that one.
My memory is great, it just doesn't seem to last all that long.......
Come to find out, Each HMI had more than one file stored on it.
Someone suggested to remove all but the used file.
It actually worked.
Dear Experts, I know that it has been a very long time since G&L products have been discontinued. But I am wondering if anybody have had any...
927
Hi, All production number reset following the comm error. I've looked through logic and disabled autamatic reset future. The counters should only...
1,930
Easy, basic question... this is my first time linking 3 ABB vfds to an Allen-Bradley PLC using ethernet IP, and the odva Drive assemblies 123 and...
2,487
Hi all ! I can't figure out how to setup the modbus RTU comm. to connect a Koyo DL250-1 CPU with a Panelview Plus 600 from Allen-Bradley. I use...
3,959
Hi, First post, I am new to this forum. I tried searching with no luck. I am using an Omron PLC - CJ2M CPU32,and I am trying to get it to...
2,395