I have two PLCs on a network. One of which is the Primary Control PLC (PLC_1). The other I wanted to use as an I-Device to serve up signals which are pulled and processed from other networked Profinet IO Device Gateways (PLC_2). PLC_2 only has one network card.

PLC_1 IP: 10.1.1.100
PLC_2 IP: 10.1.1.101
IO IP: 10.1.1.102

I have configured my IO Device Gateways. I've also created a Transfer region to/from PLC_2 to/from PLC_1. After doing this TIA Portal creates a "Profinet IO System" for PLC_1. All devices I connect up to the network automatically become assigned to PLC_1 so I cannot access the IO Device at PLC_2.

Is there a way to add another IO System where PLC_2 has access to the device and still have a transfer region where I can send data to the Primary PLC_1?
 
I think I figured it out. After connecting the IO Device to the network, I had to delete the Profinet System Connection from PLC_2, then assign it as the DP Master by right-clicking the network. This separated the two Profinet IO systems (one for PLC->PLC transfer) one for the IO device.
 

Similar Topics

is it possible to install multiple ibaPDAs on single VM or PC?
Replies
0
Views
29
Hi. I need to create several alarm servers in an application, but first I need to know if there is any impact on communication, or if more...
Replies
0
Views
62
Hello all, I know its not good practice to have duplicate destructive bits when writing plc code, but I'm wondering about writing to the same tag...
Replies
2
Views
129
Hi, Is Control Expert V15.0 supposed to support multiple monitors? I'm running Control Expert V15.0 on my host Windows 11 PC, connected to two...
Replies
1
Views
72
This is the first time I am working with Simatic Manager Step7 as I started my siemens journey with TIA which is pretty easy and do a lot of stuff...
Replies
3
Views
188
Back
Top Bottom