Door simulation lower limit switch (ls2) wiring configuration
catalinoac
Feb 2013
Cebu
  • The original limit switch wiring configuration on Door Simulation are
    LS1 = N.O.
    LS2 = N.O.
    Upon reading on the exercise, there is a "For Discussion" in which the
    the LS2 (lower) may be rewired to N.C. for "fail safe design" operation.
    <u>
    [*]Upper Limit switch wired N.O., Lower limit switch rewired N.C. resulting in:
    Upper limit switch (door open) goes False(0) when Door reaches the fully open position.
    Lower limit switch (door closed) goes False(0) when door reaches the fully closed position.
Task> Explain why this last rewiring option should result in a safer, more fault tolerant installation.
  • </u>With the wiring configuration of LS2 change from N.O. to N.C. would result in a fail-safe (OPEN CIRCUIT) protection. (As the motor will not run down if the circuit on limit switch is open)
    My question is, how about "SHORT CIRCUIT"? If LS2 will be shorted, then motor will run down (when PB closed is pressed) and will NOT STOP down to LS2 (as LS2 is shorted)
Please enlighten. Thanks
The task asks why the configuration is "more fault tolerant." Focus on the failure modes handled by one N.O. and one N.C. switch.
Your question is valid and goes down the path of performance levels in safety designs. There are devices on the market which can detect shorted wiring and faulty devices, but are more complicated and expensive than basic limit switches.
Hi guys I decide to add manual and auto mode to door simulation in logixpro since many of automated processes have manual and auto mode. I solved...
10,996
I've noticed a strange behavior with certain rotary disconnects. We all know that, if installed correctly, the disconnect interlocks with the door...
1,465
I have noticed that many HMI have a Nema rating of Mena 4/4X (indoor use only) Does anyone have any guesses as to what the constraints are that...
1,801
Our system has S7 1516 F CPU. We have doors that have contactless safety doorcontact that is cat 4 ple rated. The sensor provides us with two...
2,997
Was wondering what is everyone using for outdoor rated OIT/Panel View covers? OIT is mounted on a panel. Shade would be preferred as the panel is...
1,200