I am working in the following system and i am having the problem mentioned below please help me and solution.
System:
Allen Bradly-PLC-5 ControlNet processor(1785-L80C15).Two main processors housed in seperate I/O racks and redundant (Primary and Backup processor unit)are connected through a controlnet network and RSLOGIX5 cotrol program is used for sequence and interlocking the Lignit handling system in N.L.C.Ltd, neyveli,INDIA.
Problem:RSLOGIX5 SOFTWARE
The problem is When i am forcing the input signal in the Input table for starting the conveyor in the primary processor(node 1), The same is not updating(hotbackup) in the secondary processor(node-2). So i have to manualy do forcing in the secondary processor. Please guide me how to update forces in secondary processor automaticaly.
:) If I understand you correctly, When your online with the main processor, your not online with the hot back up processor?
When you go online with the processor, and force a bit, this is not a real world type action...I.E. the Input is actually off. So your force is only going to show up on the processor that your online with.
Using what you listed, you might want to consider putting a real world switch to by pass that input.
I've never worked with redundant processors, so I can't comment on that aspect of the problem.
I thought that forcing an input or output actually worked on the input and output cards and not the data tables. That's to say you actually have the input or output. This causes the input table to be updated because the processor actually sees the input as true. The output table will not be updated based on a force because it is determined by the results of the logic. That's why when you force an input on, you can see the rung logic update as true in logix5 and you don't see it when you force an output.
I can't verify this on a PLC5 right now. I have checked on a Control Logix system. When I force an input on, the bit value goes to 1. When I force an output on, the value stays at 0 but the force mask changes to 1.
I could use some help figuring out the layout of a Remote I/O channel Diagnostic Files in a PLC5 using RSLogix5. I've attached a screen shot of...
3,662
Hi all. I was wondering if anyone knew a way to renumber Ladder Numbers in RSLogix 5. I have deleted some of the old Program Files in my Project...
1,534
Yesterday a coworker informed me of an issue with his laptop. Anytime he opens an RSlogix5 project, and tries to go online, the entire program...
1,385
Hi Friends, 1. Please, what are the differences between RSLogix5 and RSLogix500? 2. Troubleshooting/Fault finding tools in RSLogix5? 3...
1,126
Hi , i'm looking for copy of RSlogix5 or a laptop with that software on it. I need it to upload code ,so i can rewrite it. any help would be...
30
7,939