Multiple VFD's with Varying frame sizes in same enclosure?
skyfox
Nov 2006
CA
279
Is it OK to have multiple Frame size VFD's inside the same enclosure that will be dedicated to VFD's only or is there any code/regulations against doing so?
Frame sizes will 4 A's and one D.
jraef, rupej,
Thank you both. I have never seen a VFD enclosure panel with more than one VFD inside of it(other than in pictures), at customer sites to date. On each one I have seen, there was a lot of empty space left inside of them. Sort of like parking a Yugo inside a double car garage if you will. So I read up on some NEMA specs, but didn't find anything that dictated the enclosure footprint nor did it state that only one VFD can reside inside of one. Therefore I asked the question to be sure.
Now the next question.....To cool or not to cool?
If VFD manufacturers installation guidelines are followed and proper spacing is allowed between the VFD's per their recommendations, do I still need to install a enclosure cooling fan?. The VFD Panel will be inside climate controlled plants where ambient temps will never exceed 25C (77 F). Will the VFD enclosures still need cooling? VFD's will only run the motors involved in the process for around 2 hours starlight at the most. Then, they will have a 2 hour idle time before the next cycle is started. This will continue on 24/7 basis.
Thanks again.
Yes the panel will most likely need cooling. Unless it is large enough to remove the heat generated by convection.
Decent rule of thumb is 6% of the rated duty of the VSD will be it's heat output. (100kW VSD would generate 6kW of heating).
Rittal have some free software that will calculate what you require called rittal therm.
Hi guys! I have been spending quite a bit of time yesterday and today trying to get a definitive answer to this question regarding protection an...
3,793
Hey guys , I am involved in a equipment installation process wherein the customer wants me to run multiple motors with a single VFD. I...
2,033
Good morning, A Yaskawa A1000 series VFD is controlling a chain at the ref. frequency 1 (let's say 70 Hz) as its default. In winter months, a...
1,301
Hi all, Does anyone know of a calculator for figuring out size of enclosure to house multiple vfd's? We have a job at them moment where we need...
2,244
I have an application in a dairy barn where the customer wants to run his ventialtion fans on a vfd to slow them down and get energy savings. He...
45
10,198