Topserver/ Intouch floating point value problem
pasimanninen
Jan 2008
Joensuu
22
I tryed to move 32-bit floating point number to intouch via topserver. But value seems wrong in intous value display.
Intouch show integer value correctly but floating point value is wrong if i compare value PLC vs Intouch.
Best regards
Pasi Petteri Manninen
Hello pasimanninen;
At first glance, it would seem you are facing a big-endian, little endian problem. The name refers to byte ordering in different microprocessors. It mainly causes problems with the display and manipulation of floating-point values.
I know I face this problem when I know the orignial value is 3,20 (for example) and my HMI is showing -1,2783 e-37 (also an example).
Here is a posting on Wickipedia that can explain the endian problem better:
http://en.wikipedia.org/wiki/Big_endian
If this is the source of your problem, hat you have to do is swap the bytes of the value that Topserver sends (in the PLC) before InTouch tries to output the value.
You will have to try different combinations of swapping before you get an adequate value if this is the problem.
Say that the combination ABCD represents the 4 bytes of a 32-bit register, as sent by TopServer (the original value).
Your PLC might need to read:
BADC(byte-swapping),
CDAB (word-swaping), or
DCBA (Byte and word swapping)
to interpret the original bytes as a floating-point value. You will have to try them one at a time to find out which one applies to your situation.
Hope this helps,
Daniel Chartier
Can you please explain a bit , i mean what were you expecting and what you were getting.
Value in PLC=??, value in server=??, and value in InTouch=??
Deep_arvind said:
...what were you expecting and what you were getting.
Knowing this will help us in determining what order your bytes are in and what order they need to be in so we can sort out which endian to use. Also, if you can furnish the Hexadeciaml values that will be a big help.
You need to give "###.###" for seeing those decimal points(and declare the tag as real), also if you want to display the floating values in scientific notation then there's a different procedure see InTouch help for this.if you cant get that tell me i will check that up.
Also in the min/max value(in InTouch) you should give the min or max expected value in the PLC so that they can be correctly displayed in InTouch runtime.
I am fighting with the 9030-311. ITS WINNING. I have software toolbox as my server between WW Intouch and the GE 9030-311. I can get all of my...
2,526
I cannot find anything that says that Topserver or any OPC server stores values. (except in the simulator or the Historian plug in). My...
1,591
Does anyone have experience setting up the PKTX card with topserver? i can get RSLinx to communicate with a PLC5 processor through the PKTX card...
1,522
I have a problem, I'm running an AE Licence Manager on a Windows 2016 Server, and my Window Maker is on another separate Windows 2016 Server. My...
71
Hi all. Customer wants analog faceplates really bad, even if we explained that it doesn't make much sense in his process. What he wants to see...
152